J

johnosman

I've just been testing a block of flats where the main water supply is plastic and goes through the block in plastic pipe, the issue is that all the flats are then fed via a meter and copper pipework. Should there be a main bond to the closest copper pipework to the main water intake and this then joined to every subsequent branch off of the plastic pipe?
 
1st step is to test it. disconnect any other bonding and IR test from copper pipes to MET. if the reading is > 22kOhms, then don't bond it.
 
1st step is to test it. disconnect any other bonding and IR test from copper pipes to MET. if the reading is > 22kOhms, then don't bond it.

Wish you luck in not encountering parallel earths in a block of flats!! Best just to bond where you can, if metallic pipework is still part of the service installation!!
 
I did post a nice reply, but the system crashed on me again with usual message...

Mine crashes from time to time, but my reply box auto saves what i've written so if after it crashes, i come back hit the auto save and hey presto it's all back ready to continue writing, or post!!
 
clever sod! LOL. :45:

where's auto save?
 
clever sod! LOL. :45:

where's auto save?


Only appears in the bottom left hand corner of the reply box when text has been saved. On my reply box as i'm typing this, a little yellow box on the right hand corner, fades in and out stating ''Auto Saved''!! I can't be the only member with this facility, ...perhaps you just haven't noticed it!! lol!!
 
Which can often be a nightmare. Gas may be extraneous, then connects through the boiler to the water pipework and hey presto, the water pipe is effectively bonded via the gas 10mm, but may not in itself be extraneous...so, unless you can isolate the gas from the water by disconnecting pipework, there's often no way of knowing for sure whether the water pipework is actually extraneous...
 
Also in flats look out for borrowed earths as this is getting found more ie the guy upstairs has an earth but the guy below him does not yet is getting an earth from him via the gas & water bonding
 
As it the main incoming water it should be bonded and extraneous shouldn't come into it, if it was just one property and the water came into the building in plastic and then went to copper you would bond it without even thinking about it, so in this instance should you do as I first thought and go to the closest copper pipe to the main stopcock and then link across to the rest. Or do you know different....lol
 
As it the main incoming water it should be bonded and extraneous shouldn't come into it, if it was just one property and the water came into the building in plastic and then went to copper you would bond it without even thinking about it, so in this instance should you do as I first thought and go to the closest copper pipe to the main stopcock and then link across to the rest. Or do you know different....lol

Why is that then?
 

Reply to Main bond to water supply to block of flats. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
Hi all, I've installed a Tesla Gen 3 wall charger supplied by my client. For your information, the place that I installed is in a block of flat...
Replies
2
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
796

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock