Discuss Main Bonding csa when earthing csa calculated in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

timhoward

-
Esteemed
Arms
Supporter
Reaction score
8,765
Just double checking please - in situations where the main earthing conductor csa is calculated, and in a TNS installation, the 50% bonding conductor csa rule still applies to your final calculated and rounded up earthing conductor size? (As opposed to the tabulated size)
I'm doing remedials and someone else gave a C2 for the main earthing only being 6mm csa as line conductors are 16mm, and also gave C2 and said the 6mm csa main bonding should be 10mm. It is very definitely TNS.
However the formula confirms that in fact 6mm earthing is fine (it's a sub main with C32 breaker protecting it and low PFC), and as long as the 50% is based on the 6mm I can't see why the main bonding is an issue either.
 
In fact more complex. Looked more closely now.
16.0 cpc as far as adaptable box (one core of SWA). 16.0 cpc to an MET block. 10.0 cpc from MET to CU.
Bonding conductors to gas, water are 6.0
 

Reply to Main Bonding csa when earthing csa calculated in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
671
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
786
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock