hi, just looking for some help on how to install the main bonding on a large industrial building.
Firstly the supply neutral to the building is over 150mm so am i correct thinking i need to use 50mm bonding conductors for water etc?
Secondly the MET is about as fair away as possible on this site, there are MCCB boards all over the place with a 70+ earth to them and tray mounted earth bars with 50+mm earth to them, as long as i verify these are still connected can my bonding conductors come off of these?
I also need to install the bonding in another building on the same site for structural steel, water and hot water, the supply at this building is 25mm with a 70mm earth, what size bonding conductor do i need to use here? and can i just take it from the distribution board?

Any help and i will be very grateful, as ive never worked on a site this size and am pretty much lost in regards to what i can and cant do,

thanks
 
im unsure at the minute, il try and find out for tomorrow morning. I know theres 8 11kv transformers on site, dont know if that tells you anything?
 
Thanks, what about the other seperate building on the site with the 25mm²?
Sorry forgot about that.
I don't understand why the earth is so much bigger than the supply, is it a typo?
If it is a typo, and the supply is 125mm², then both systems would require 35mm² bonding conductors.
If it isn't a typo, and the supply is only 25mm², then with TN-C-S, you would only require 10mm² for bonding.
If TN-S, you would have to verify the correct size earth is being used, one would normally expect the earth conductor to be only 16mm², with 10mm² bonding.
If the 70mm² earth is correct, you would need 35mm² bonding.
 
Last edited by a moderator:
If it’s an industrial site you can near guarantee it will be TN-S.
As to the 70mm earth I don’t know why. The company if first worked for 16 & 70mm was always on stock, anything else had to be ordered, could be a similar situation. It’s what they’d got so it got used.
 
Last edited by a moderator:
does anyone know if i can connect the bonding conductors to the tray mounted earth bars/MCCB board terminals? And if so would i need to trace the cables back to the MET and fit a 'safety electrical connection do not remove' tag at each connection? Everything ive read always say to take them to the MET but the actual METs are about as far away as possible on this site from all the stuff that needs bonding
 
I would connect a seperate earth bar to the earth terminal at the panelboards, and create an Earth marshalling terminal. This is very common on industrial sites ive worked on, and its the way that we bond the pumping stations and treatment works.
 
malc mentioned about steel frame earlier. He is hinting at the fact that it is permitted to use any extraneous metalwork as bonding or indeed CPC, provided precautuions are taken against its removal, and it is of a suitable CSA, which 90% of steelwork on a building will be.
 
Does this mean for say a ducting system i could take a bonding conductor from the structural steel to bond the ducting or did i misunderstand? sorry about all the questions but im pretty new to working in places like this and im quite interested in it.
 
yes you can. It must be labelled as usual, and of course the steel must be bonded to the main earth to the building. I would guess that it will be, but its worth checking.
 
yes you can. It must be labelled as usual, and of course the steel must be bonded to the main earth to the building. I would guess that it will be, but its worth checking.

i never knew that, that makes life a hell of a lot easier now though thanks, the structural steel is bonded in about 240mm. When you say precautions must be taken against its removal is that just as simple as labeling it?
 
the bonding connnection should be labelled with a label not less than that of a BS951 clamp. other precautions are things like not connecting to steel that is likely to be removedand maybe enusring that removal of any cable in the building by non sparks requires the permission of the electrical engineer.
 
If the building is all structural steel and has been bonded back to the MET at origin, you can safely say that the whole of the steelwork is one big bonding conductor that is interconnected by cross beams and sections etc!! haha!! Just try isolating all those parallel earth paths, ...no chance!! The chances are, that the structural steel of these buildings is also forming part, if not all of the earthing for the site too.

As you say, ...you can just link the steelwork to the system or service you want to bond out. In reality, the chances are it's already bonded by fixings etc,, but you will still need to make purpose made bond connections, to satisfy all the various requirements you have these day's...

Be interesting to know what sort of Ze and/or Zs values you get at the buildings incoming supply point??
 
When bonding the steel work use clamps for the connection or weld a bolt on, don’t drill structural steel. If you weld a bolt then put it inside the web out of harms way.
 

Reply to Main bonding in large industrial building in the Canada area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
675
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi wondering if you could help with some advice Been running an Essex/suffolk based electrical firm for last 20 years, mainly light commercial...
Replies
1
Views
549
Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...
Replies
17
Views
2K
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
944

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock