Discuss main bonding to water pipe? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
A
aaronstuart
Hello all,
Mains incoming water pipe has been altered, there is about 12-15 inches of coppper pipe entering from the ground into the kitchen then around 3 - 4 mtrs plastic pipe before going back to copper piping, do I still need to bond the pipe and also a link between the plastitc to make continuity?
Thanks Aaronstuart..
Hi,
Regulation 544.1.2 states that any bond shall be made as near as practicable to the point of entry of that service into the premises. It then talks about if there is an isulating section to place the bond after that, and before any branch pipework. In my opinion i would do as you said, bond at the point of entry and branch it across the plastic to the continuing metal service. This would cover any eventualities in the future, of say, the plastic pipe section being changed backed to metal again. Also, if you didnt apply bonding, can you be sure there will be no other potential introduced into the building, from say, water pipes connected to the same system running under ground to an outside boiler house etc? I came across the same situation while doing a PIR, and quoted the above as observations on page 2 of the cert. Its better to make an observation rather than someone ask why didnt you make that observation! hope this helps. :)
ps. wow my first bit post!
Reply to main bonding to water pipe? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Hello, I have 50 ft of corrugated pipe buried between my house and a pool shed. I placed it where I knew future landscaping would make it very...
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
I found myself needing to do some emergency plumbing at home this evening. I've got a small guest flat on my property which has been empty for...