Discuss Main breaker trip in the UK Electrical Forum area at ElectriciansForums.net

tank

-
Reaction score
16
Hi guys, why might a fault on a final circuit in an apartment trip the dp c63 submain circuit breaker in the plantroom but not any mcbs on the consumer unit in the apartment?
 
A kitchen fitter did something which took out the breaker in the plantroom but not any mcbs on the consumer unit in the apartment. I insulation resistance tested the submain and it was fine.
 
If the fault current was high enough to achieve instantaneous tripping on both devices, it's a coin flip which one goes first.

MCBs are notoriously poor for achieving effective discrimination/selectivity and are often installed in-line as a product of poor design and nothing more.
 
same thing with this 3A fuse for bathroom fans crap, when they are on a 6A MCB protected circuit. the MCB is likely to trip instead of (or as well as) the 3A fuse.
 
Typically you need the fancier electronic type of MCCB that allows a short delay before firing (at least up to its own high instant magnetic trigger point) to allow any chance of good selectivity - i.e. if a down stream fault occurs then it only trips the downstream breaker.

MCBs in series rarely have much selectivity. Often it is barely more than the instantaneous trip of the upstream one, so if you have a 63A C-curve breaker that is 315-630A. Hence if the fault impedance is below 0.73-0.36 ohms then the upstream one probably goes as well (since it is already underway to trigger before the downstream MCB contacts have opened).

Or you use a fuse up-stream. Then you typically need a far bigger PFC to blow it, and might even get total selectivity.
 
Re-reading the OP's post, it would be very unusual for the downstream one not to fire. It would have to be seized or contacts welded shut (which is very bad news in any circumstances).

Personally I would suspect the cable-drilling culprit rest the breaker hoping all would be well and then found out the upstream one had gone.

But just in case I would check all MCBs toggle normally, and check if there is any chance of the supply tails being drilled, and look carfully in the CU in case some absolute moron has taken a cable from the busbar side of the MCBs.
 
Very unlikely (more a USA thing), but they are not Federal Pacific / Federal Electric ones by any chance?

I have heard various horror stories of them failing to fire on faults, thankfully never met one myself.
 

Reply to Main breaker trip in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Could the sun’s heat on a caravan mains supply cable cause the fuse/circuit breaker at the meter box/supply end to trip?
Replies
20
Views
1K
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
727
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
277
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
709
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock