Discuss Main earth conductor?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
E
essexboy
hi all thanks reading my post
i have just changed a Cu and intend on using the job for my elecsa inspection i have up-graded the meter tails from 16mm to 25mm ,the earth conductor ( TN-S ) looks like 6mm and needs to be upgraded to 16mm ,but who should be up grading the earth conductor?? is this down to the dno?? or should i just upgrade from the cu met to the met outside the cu ??
If the mec is terminated to the incommer lead/sheath I tend to cut it to a short length & terminate into a met/block (with a 951 label fixed to it) that I fix to the meter backboard. From this met I run 16mm to the cu.
Then advise the customer (backed up with a letter sent with certs) that they need to contact dno to upgrade the mec.
"Then advise the customer (backed up with a letter sent with certs) that they need to contact dno to upgrade the mec."
Probably wont upgrade as they will claim that it is sized by calculation. If you use the adiabatic equation to check you will probably find that the 6mm is ok, but best to use EasyFox's installation method.
yeah it is appropriate but when your viewing threads you know who people are by there avatar (i do anyway!) Easy's easy going but dont know if you might be better finding sommat a little bit different? lol
how bout this
blimey thats big!!
Reply to Main earth conductor?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Morning guys, Just been to look at a CU change and there was a bit of an oddity with the PME connection in the old black cut out. Looking at the...