Hi,

I have recently carried out a periodic test and inspection on 1960s purpose built flat. The means of earthing was via the main gas pipe connected by earth clamp before the gas meter.
Is this acceptable under BS 7671 2008? I had a Ze reading on 0.19 ohms.
 
542.2.4 says no

metallic pipe work used for water supply maybe used if precautions are taken against its removal
 
Last edited by a moderator:
Hi,

I have recently carried out a periodic test and inspection on 1960s purpose built flat. The means of earthing was via the main gas pipe connected by earth clamp before the gas meter.
Is this acceptable under BS 7671 2008? I had a Ze reading on 0.19 ohms.

Are you serious??
Just to clarify Kinky's post ,it is not acceptable to use a public water supply pipe as a means of earthing.Only private pipes may be used as an earth electrode with the precautions stated above.
 
Last edited by a moderator:
Hi,

I have recently carried out a periodic test and inspection on 1960s purpose built flat. The means of earthing was via the main gas pipe connected by earth clamp before the gas meter.
Is this acceptable under BS 7671 2008? I had a Ze reading on 0.19 ohms.

Thats a wind up isnt it , surely ?
 
Hi,

I have recently carried out a periodic test and inspection on 1960s purpose built flat. The means of earthing was via the main gas pipe connected by earth clamp before the gas meter.
Is this acceptable under BS 7671 2008? I had a Ze reading on 0.19 ohms.

Surely that's a wind up, though.

If the DNO gave him TN-C-S now, with the regulation 0.35 Ze, and he bonded that gas pipe (as you do:)) - most of the installation's current is going to be flowing down that gas pipe.

Or am I missing something??
 
Wayne the tncs will probably [but not always] be less than 0.35 ,and there will always be the case of parrallell paths to extraneous conductive parts in the event of a fault to earth, so i dont think that is a major issue. the issue is not having a suitable earthing facility at present. Must say though that if the op has to ask the question then maybe he should consider some training, cos its a fundamental part of I & t to know the answer.

sparkylad.
 
Wayne the tncs will probably [but not always] be less than 0.35 ,and there will always be the case of parrallell paths to extraneous conductive parts in the event of a fault to earth, so i dont think that is a major issue. the issue is not having a suitable earthing facility at present. Must say though that if the op has to ask the question then maybe he should consider some training, cos its a fundamental part of I & t to know the answer.

sparkylad.

My thoughts exactly.....If you have to ask whether it is acceptable to use a gas pipe as a main earth you do not have sufficient knowledge to be carrying out a PIR.
 
Wayne the tncs will probably [but not always] be less than 0.35 ,and there will always be the case of parrallell paths to extraneous conductive parts in the event of a fault to earth, so i dont think that is a major issue. the issue is not having a suitable earthing facility at present. Must say though that if the op has to ask the question then maybe he should consider some training, cos its a fundamental part of I & t to know the answer.

sparkylad.

Yeh, my point was that it seemed awfully low - surely that's not the kind of reading I'd get if I did a Ze test on my gas pipe.

Let's take a good TN-C-S system with a Ze of 0.19 ohms - are you telling me that a bonded gas pipe would offer the same impedance back to the transformer as the supply neutral conductor connected to the star point?:)

Either there is another means of earthing or he's measured it wrong...... or it's a wind up

I wasn't talking about an earth fault, by the way.

I was talking about the normal operating current taking this path as oposed to travelling down the neutral(of higher impedance)
 
Last edited by a moderator:
Oh. Got you now wayne ..sorry , yes I get the point you are making, and yes the op unfortunately does not inspire great confidence in his I & T ing prowess so he may well indeed missed some other means of Earthing or Bonded Extraneous part such as a mettallic water pipe etc.
 
Your sure that is the main earth to the flat?

Have you tried to do a Ze on the remaining earths in the MET? I can understand older houses having relied on the use of a Metal pipe for an earth but a 1960s flat? What floor was the flat on and was there a communal cupboard with the main incoming supply for the building in there?
 
Yeh, my point was that it seemed awfully low - surely that's not the kind of reading I'd get if I did a Ze test on my gas pipe.

Let's take a good TN-C-S system with a Ze of 0.19 ohms - are you telling me that a bonded gas pipe would offer the same impedance back to the transformer as the supply neutral conductor connected to the star point?:)

Either there is another means of earthing or he's measured it wrong...... or it's a wind up

I wasn't talking about an earth fault, by the way.

I was talking about the normal operating current taking this path as oposed to travelling down the neutral(of higher impedance)

It could be that he was measuring a gas bond with a common pipe to other flats and the reading of 0.19 was via the other flats gas bond to their met
 
This was my thinking - That's why I am wondering where the main incoming supply is. Whether there is one main supply cable split to individual meters for each flat or if they all have individual cables. Round my way especially its unusual to get flats that all have an individual supply cable coming into them. They normally have one massive supply cable that feeds meters for each flat (That probably makes very little sense to people reading but its clear in my head!).
 
A gas pipe or water pipe should not be used as a means of main earthing for one common sense reason, the same reason the behind the BRB regulation. Irrespective of whether you get a good Ze measurement or not you can't guarantee that this will always be the case because water/gas companies can and do disrupt/upgrade their supply pipe. ie to plastic pipes
 
Lol, but was rewired in 1968 by YEB using the same regs I fear. Meter board was held against wall of cellar by a 4" x 4" chump of wood jammed in there.
 
Possibly not - owned a house in Leeds from the Victorian era where main earth was gas pipe - clamped on the customer side of the meter too....

Had similar thing in my house. There was no earthing conductor.

Only path to earth for the entire property was via the bonds to gas & water mains.

Gas bond was after the meter andf the incoming water was plastic.

o dear
 

Reply to Main earthing by gas pipe. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
I am due to carry out an electrical job in a third floor flat. Incoming supply is TN-S. Cannot locate a main earthing conductor inside the CU on...
Replies
4
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock