Discuss Main earthing by gas pipe. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

I wasn't talking about an earth fault, by the way.

I was talking about the normal operating current taking this path as oposed to travelling down the neutral(of higher impedance)

Huh? Why would any current other than slight leakage be flowing in the earth in normal operating circumstances?

Both conductors are going to be completely separate upstream until you hit the supply in a TN-C-S system, so surely unless you have a neutral-earth short circuit then there would be no path for the current to get on the earth? :)
 
Huh? Why would any current other than slight leakage be flowing in the earth in normal operating circumstances?

Both conductors are going to be completely separate upstream until you hit the supply in a TN-C-S system, so surely unless you have a neutral-earth short circuit then there would be no path for the current to get on the earth? :)

But if you bond the gas pipe (with the 0.19 ohm Ze) to the MET, the MET is connected to the neutral at the service head.

So when the normal operating current of the installation flows down the neutral to the service head, it has a choice of path back to the transformer......down the neutral (Ze 0.35) or down the Earthing conductor/Bonding conductor/gas pipe (Ze 0.19).

Where do you think most of it will go?:)

This is why losing the supply neutral on a PME (PEN) system is so worrying.

And this is why I said 0.19 was awfully low for a gas pipe.
You will always get some current flowing down the parallel paths, but it shouldn't be anywhere near that amount.:)
 
But if you bond the gas pipe (with the 0.19 ohm Ze) to the MET, the MET is connected to the neutral at the service head.

So when the normal operating current of the installation flows down the neutral to the service head, it has a choice of path back to the transformer......down the neutral (Ze 0.35) or down the Earthing conductor/Bonding conductor/gas pipe (Ze 0.19).

Where do you think most of it will go?:)

This is why losing the supply neutral on a PME (PEN) system is so worrying.

And this is why I said 0.19 was awfully low for a gas pipe.
You will always get some current flowing down the parallel paths, but it shouldn't be anywhere near that amount.:)

Hmm, I like you, you make me think!! :D

I doubt very much that the earth is actually 0.19 ohms, as it is just a large earth electrode, so methinks the test has been wrong or this is due to parallel paths somehow...

I agree with losing the neutral on a PME supply, but that's why it's an ME and not just an E.
 
Hmm, I like you, you make me think!! :D

I doubt very much that the earth is actually 0.19 ohms, as it is just a large earth electrode, so methinks the test has been wrong or this is due to parallel paths somehow...

.

I think Des probs hit the nail on the head with post #15
 
My thoughts exactly.....If you have to ask whether it is acceptable to use a gas pipe as a main earth you do not have sufficient knowledge to be carrying out a PIR.

*******Removed******* I knew it wasn't acceptable for BS7671:2008 but the wiring was over 60 years.
 
Last edited by a moderator:
So you haven't been around for nearly 3 years, and come back having a rant at a respected member, for making what was a valid observation!!

See you in another 3 years then!! lol!!
 
So you haven't been around for nearly 3 years, and come back having a rant at a respected member, for making what was a valid observation!!

See you in another 3 years then!! lol!!

I have been around I have just had better things to do then spend time on here. I am in a band now that is doing very well and I only found your quote as I was carrying out a google search for something else. I am so glad I do not have work in the electrical/building trade any more. You my be a respected member on here but you a definitely not respected by me.

*********Removed********

Btw to all you other members re the gas pipe, it was a very old 3" in diameter one that was in a 1930's purpose built flat in London. This is why I think the readings were low due to the size of it and parallel paths. Thank you to all of you that responded to me in a helpful manner.
 
Last edited by a moderator:
I am so glad I do not have work in the electrical/building trade any more. You my be a respected member on here but you a definitely not respected by me.


Just as well you're out of the industry, if you actually left the installation as was, without a primary means of main earthing!!

In a Band now eh, so now probably on a constant high, on wacky baccy or stronger, .....another flash in the pan musician that think what they have to say, is somehow more important than any others opinion!! lol!!
 

Reply to Main earthing by gas pipe. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
I am due to carry out an electrical job in a third floor flat. Incoming supply is TN-S. Cannot locate a main earthing conductor inside the CU on...
Replies
4
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock