Domestic TNCS, main earthing conductor runs to water pipe, bonds via clamp with label, cable is continuous, then runs on to MET in DB.

Seems wrong, but cant find specific reg to say so....any thoughts?

Thanks,

Timotei
 
Its an earthing conductor not a main protective bonding conductor. Part 2 definitions. Fig 2.1.

But I can't see anything specifically prohibiting it.
 
I think @Wilko has it with the Ze problem. And looking at 542.4.1 (18th) it states an MET shall be provided...
and at 542.4.2 ...To facilitate measurement of the resistance of earthing arrangements...
So checking bonding requirements and Ze would be a bit of a conundrum and it could be argued unless there is separate MET complying with the former reg. then it would not comply?
 
I think @Wilko has it with the Ze problem. And looking at 542.4.1 (18th) it states an MET shall be provided...
and at 542.4.2 ...To facilitate measurement of the resistance of earthing arrangements...
So checking bonding requirements and Ze would be a bit of a conundrum and it could be argued unless there is separate MET complying with the former reg. then it would not comply?
I have agreed with you, though if the clamp to the water pipe is easily accessible and the conductor is continuous then measuring the Ze may not be a major problem. Not ideal though, I agree. I would definitely look at running in a separate conductor, just in case wet pants comes along and does some pipework alteration and decides to just cut through the cable.
 

Reply to Main earthing Conductor also bonds water in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
664
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
735
I am due to carry out an electrical job in a third floor flat. Incoming supply is TN-S. Cannot locate a main earthing conductor inside the CU on...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock