Discuss Main protective bonding conductor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

A

Adz

Hi,

Recently i carried out a periodic inspection report. It was on a house that had a separate boiler house. The boiler house had a light, a few spurs for the boiler and heating pump. It was an oil fired boiler and i placed a defect on the report as the incoming metal oil supply pipe had no main protective bonding conductor to it. Am I right to defect this? One of my bosses said it wasnt necessary to defect it as "it was a separate building" however i still disagree. What do you think ? :confused:
 
seperate building = seperate supply = seperate test

if the oil supply pipe goes into the house it should have a bonding conductor run from within 600mm of entering the house and running directly back to the CU or MET

from the point of entry into the house is your concern, this is the equipotential zone in theory. but in your circumstance i would say that if the sockets are supplied from the house therefore they are a part of your inspection ande the CPC extends the equipotential zone and the tank should be bonded as it has the potential to become live under fault conditions.

the code 4 is a personal decision, you being the competent person are the duty holder throught the test/inspection

is there an earth spike on the tank or any of the supporting framework? if not i honestly think you'd be justified to add it as a code 1, bonding conductors are a neccessity, end of!
 

Reply to Main protective bonding conductor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
649
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Replies
2
Views
859
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
889
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock