If it's the 'main' CU for a installation of several circuits, then the answer is no, for the reasons given above, but for things like a 2W or 3W CU added on for a couple of extra circuits, such as a shower, or for a small garage CU, it's perfectly acceptable.
 
Is there any good reason why you shouldn't use an rcd as a main switch in a domestic installation thats tns/ tncs ?
To me there are two separate questions here:
  • Can a RCD act as the main isolation switch?
  • Is it acceptable to have one RCD for 30mA "additional protection" of all circuits?
For the 1st point, then yes the usual double-pole RCD can be a main switch providing it is rated to at least the maximum system current. So on a 60A fuse the RCD should be 63A or more, etc. Sometimes you will find the sum of MCBs is lower than the supply fuse, so that is another means for limiting total load to the RCD's rating.

For the 2nd point then I would say no, it is poor practice as everything goes off on any trip and as that includes all lights, a safety risk as well. Additionally the accumulated leakage of a whole installation makes spurious trips far more likely to happen.

TL;DR Fine for a 100mA or 300mA delay incomer (as used for TT or farm/fire risk, even if supply is TN) where you have separate groups of 30mA protection, poor for general use except for a very small installation.
 
To me there are two separate questions here:
  • Can a RCD act as the main isolation switch?
  • Is it acceptable to have one RCD for 30mA "additional protection" of all circuits?
For the 1st point, then yes the usual double-pole RCD can be a main switch providing it is rated to at least the maximum system current. So on a 60A fuse the RCD should be 63A or more, etc. Sometimes you will find the sum of MCBs is lower than the supply fuse, so that is another means for limiting total load to the RCD's rating.

For the 2nd point then I would say no, it is poor practice as everything goes off on any trip and as that includes all lights, a safety risk as well. Additionally the accumulated leakage of a whole installation makes spurious trips far more likely to happen.

TL;DR Fine for a 100mA or 300mA delay incomer (as used for TT or farm/fire risk, even if supply is TN) where you have separate groups of 30mA protection, poor for general use except for a very small installation.
nice one
 
In this case, I guess you should use a type A rcd or type F , rather than the more common type AC.
Realistically type AC ought not to be made any more (or even for last few years) as so many products have some capacity to leak an element of DC.

As @ImpededLoop says most RCBO (at least all I have seen in recent years) are type A which ought to be your base line for RCD/RCBO choices.
 
There are excellent answers above which I agree with.
It's quite common (in my area at least) to find a semi-rural row of 2 up 2 down terraces with overhead supply, TT earthing, and a fairly old 5 way consumer unit with an RCD main switch.
My additional comment would be that the chances of pressing the test button are (even) lower than the usual 0% if you lose all power at once by doing so, and RCD's need occasional exercise to continue doing the job they are designed to do. To my thinking there is an increased risk of the RCD not working when it's the main switch as it's probably sat there untested most of it's life.
 
RCD's need occasional exercise to continue doing the job they are designed to do.
Agreed! If never tested you have no idea if it would detect a fault and even if it does, would the mechanism actually trip OK.
To my thinking there is an increased risk of the RCD not working when it's the main switch as it's probably sat there untested most of it's life.
If I were installing a CU for a TT system it would be a 100mA delay RCD as incomer and RCBOs for the individual circuits. Sure the 30mA protection might have failed so you don't have proper shock protection, but a 100mA delay is better than nothing and it prevents the CPC/earth rod sitting at 230V as would otherwise happen if the only RCD failed to trip So whole-house ADS is far better than none at all!
 

Reply to Main Switch twitch...... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, if I cannot access the line side of a crabtree 100A DP main switch. Would someone enlighten me how to conduct safe isolation on this...
Replies
15
Views
1K
Good evening, I wondered how the MCB between RCD and the Main switch is wired while watching this video. Photo attached. I assume a busbar link is...
Replies
3
Views
832
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
971
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
415
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock