foghorn

HI ALL
whilst completing certificate on pirform having installed a shower consumer unit with a 40A 30ma rcd and mcb
nominal current rating of main switch in relation to overcurrent protective device (ie) main switch is rated aty a lesser value than main over current protective device, supply characteristics 100 amp bs1361

any ideas how to get round this
 
less than 1 metre away from cut out meter tails into rcd shower circuit into mcb pirform saying fail due to main cut out fuse higher rated than rcd on shower box so says fail on choice of protective device for fault protection/overcurrent protection i know that the circuit is covered by this due to mcb however certificate says fail cos main switch is of lesser value in relation to cutout fuse
 
whilst completing certificate on pirform having installed a shower consumer unit with a 40A 30ma rcd and mcb nominal current rating of main switch in relation to overcurrent protective device (ie) main switch is rated aty a lesser value than main over current protective device, supply characteristics 100 amp bs1361

any ideas how to get round this
Stop calling it a Main Switch.

It's no different than any of the other RCDs in the installation.
 
ok then rcd however other consumer units do have 100amp main switch then rcd the shower boxes come with rcd then mcb so in relation to cut out fuse is a fail yes
 
Mmmm did listen mate and yes is not fail with MCB alongside however the perform certificate says fail because of main cut out fuse in relation to RCD
 
In PIRform, go into the intelligence manager for the cert and suppress the comment. Then go the schedule of inspections and change the relevant box to 'PASS'. (Might have to do a save in between.)
 
Mmmm did listen mate and yes is not fail with MCB alongside however the perform certificate says fail because of main cut out fuse in relation to RCD
you can fuse a cable down each end....the OPD for the shower will take care of any short circuit....the RCD will take care of any earth fault...
jesus wept....
 

Reply to main switch versus OPD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
BACKGROUND I live in a small town where it is difficult to find ceritified electricians. In fact, electrician certification is not common for...
Replies
1
Views
1K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K
Looking for some advice on what I've discovered is the electrics situation in my rental property. I'll note that before I moved in here I made...
Replies
118
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock