Discuss Mains cable from supply to consumer unit in the UK Electrical Forum area at ElectriciansForums.net
Hi, have a metre box 4m away from consumer unit, there is going to be an extension on the side adding an extra 4m so the metre box is getting moved to end of house again. Total length will b 10-12m, at the min the 25mm tails are going from mains to fuse switch with an 25mm 3core swa supplying the consumer unit. I’ve said he’ll have to basically run a new 25mm swa from the fuse switch by the mains to the consumer unit. Correct?
How come I get a 'Dislike' @Charlie_ ?
I cry when people don't like my posts... :sob::sob::sob:
Ta mate...
Ohh so sorry
Thanks for bringing that to my attention..
I am currently using my phone, winding down drinking a beer and my thumbs are slightly misfiring
Let you off mate. I can stop crying now.
Does it really need a 25mm SWA from the switch-fuse ? Unless there are a couple of electric showers,all electric heating and cooking I'd be considering 16mm and a 63a cartridge in the switch-fuse, 25mm is a pain to work with in a domestic setting.
Wouldn’t using split concentric and installation method, make it more likely ending up with RCD protection?
Agree MW, reading 522.6.202 it is possible to run cable in a wall at less than 50mm and not use an RCD. But the cable must be in a zone and must comply with 522.6.204, which includes a list of qualifying cable specs (among other methods). I think split con is BS4553-1 and it's not on that list. However SWA (BS5467, BS6724 and BS7846) and Pyro (BS60702-1) are on it.
Reply to Mains cable from supply to consumer unit in the UK Electrical Forum area at ElectriciansForums.net
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
4K