Mains Leads.
I supply machines that are 21 amp per phase. the CE certification states a 2.5 5 core lead should be fitted. Which we do.
I have been asked to fit 4.0mm because the mains breakers are 32 Amp.
Isn't this the wrong way round? if the fuse was bigger it makes no sense to fit a bigger mains lead as the machine is still 21 amps per phase.
I supply machines that are 21 amp per phase. the CE certification states a 2.5 5 core lead should be fitted. Which we do.
I have been asked to fit 4.0mm because the mains breakers are 32 Amp.
Isn't this the wrong way round? if the fuse was bigger it makes no sense to fit a bigger mains lead as the machine is still 21 amps per phase.