Hi guys,
Im just filling in my first ever solo EIC when I check the onsite guide and gn3 for max permitted zs (tabulated) for bs60898 type b 32A the table shows 1.16ohms but to me it didnt ring a bell, checking bs7671 table 41.3 shows max zs to be 1.44.

Can anyone shed some light on why and which I should use as the tabulated value?

Regards,
Simon
 
the osg figures allow for resistance increase of cable when operating at a higher temperature. i.e.70deg. as opposed to the 20deg. that you are measuring at. as the sotr asks for the max. figure, i always use the bgb values. never yet seen a cable running at 70deg. under normal conditions except on some industrial applications.
 
i did 6 months 500ft. down the salt mine. it was a constant 10deg. summer and winter. working in tee shirt. best thing was... it never rained.
 
haha. took 45 minutes to get out to the van and back. deliberately left something behind as it was a perfect excuse to get out and have a smoke. boss got wise after a while and decreed that anything i was short of, i'd have to do without till break time. bugger.
 
You would think with a salt mine everything would be red rusty, not a bit of it, the air’s to dry.

Did you see the grave yard? All the machines taken down there, worked to death and then just dumped in a corner.
 
everything did go rusty. we were using 10 cans of wD40 a week, spraying tools.
 

Reply to max measured earth loop impedance query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Can someone explain this to me? The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.
Replies
6
Views
3K
Hi I'm looking at Table 7.1(i) in the On Site Guide. Max length of cable runs. In some cases where there is no RCD protection the length is...
Replies
4
Views
1K
Morning all. So just trying to refresh my grey matter but having a biff moment. Earth fault loop impedance with circuits protected by BS EN60898...
Replies
4
Views
2K
hello all could anyone help me i am doing my 2392 and i am a little stuck i have been asked a question which is using the following measured value...
Replies
3
Views
2K
Deleted member 105166
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock