Prospective Short Circut Curret.
Now , if you measure the impedance on a installation P to N , and get a reading of 0.21 OHMS , the max current flow between these two points P and N will be 230/0.21 = 1095A.....1KA.
Now if you have 3 phases , and each are the same impedance P to N , the the max will be 1095A per phase , correct?
Now , if all 3 phases are shorted together , will this value still be the same , ie 1095 will flow from each phase , as the phases are 120 deg out of phase , will some of the current flowing from each phase , be actually some of the other , but the max will be 1095 through the MCB?
Say for instance a P to P fault with a 0.21 Impedance from each Phase to N.
Would 1095A flow from each phase , say in a RED to WHITE fault , 1095A would flow , BUT 1/2 the current that flowing in red is actullay some of whites , and in white its some of reds? ...
The same prinpical as normal operating current of a 3 phase motor?
Please Help!
Craig.
Please Help!
Craig.