Would anyone know the max tripping time for this earth leakage device?
I’m guessing 500ms it’s time delayed but I know that figure is for RCDs and RCBOs, I tested it at 560ms
Thanks1F7E803A-A617-42B0-8EE1-8C9782718227.png
 
Last edited by a moderator:
Up to 3 seconds - turn the dial to 0, 0.3, 1.0 or 3.0 seconds - it is set at 0.3 secs in your photo.

it's also set to 0.3A (range 0.03, .3, 1 & 3A) so what was your test current?
 
Yes set to 300ms time delay, it tripped at 560ms
[automerge]1584603181[/automerge]
Up to 3 seconds - turn the dial to 0, 0.3, 1.0 or 3.0 seconds - it is set at 0.3 secs in your photo.

it's also set to 0.3A (range 0.03, .3, 1 & 3A) so what was your test current?
Set to 300mA on tester and then set to (S) which is time delay
[automerge]1584603200[/automerge]
Is it not set to 0.3S ?
Yes it is
 

Reply to Max Tripping Time in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
There are 2 inverters feeding into a dorman smith C16 rcbo , every time I visit this site (communal area power) it has tripped. it switches on...
Replies
13
Views
2K
Hello, as a relatively newly qualified electrician (mature trainee who completed his NVQ in 2023) today was the first time I've seen a melted...
Replies
11
Views
890
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
4
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
627

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock