Discuss max Zs for delayed RCD's in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
R
rasell
The regs give a table for non delayed RCD's and circuits under 32A, how do you calculate max Zs if there is a delayed RCD or if the circuit is over 32A?
A 30mA time delayed RCD still trips with a fault current of 30mA it just takes a little longer and so Zs on a 30mA RCD is 1667 ohms
Table 41.6 (page 54) gives circuits up and including 125A and also a formula for anything over that.
Reply to max Zs for delayed RCD's in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Still having a discussion @ work about this…TNCS system DB/CU is a split 30ma RCD configuration,5/5 MCB’S are 60898 what Max Zs would you put in...
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...