Discuss Max zs readings for TT in the UK Electrical Forum area at ElectriciansForums.net
Max Zs permitted is the maximum value that the OCPD need to trip. It is not the DNO value or the 200 ohm stable value.
There is no requirement for Zs to be of a value to operate the OCPD within the required time in the event of a fault to earth. The preferred means of earth fault protection on a TT is an RCD (411.5.2) and the maximum Zs value will be in accordance with table 41.5. (411.5.3).
The maximum value whether you like it or not is 1667 ohms for a 30ma RCD and that is the value to be recorded on a cert for a 30ma RCD.
Yeah that is what I said ‍♂️
I go by what the dno insist on and the only figure that is realistically acceptable <200
Which DNO insists on less than 200?
I've never heard of this before and considering the DNO have nothing to do with a consumers own earth electrode I don't see how it's any of their business getting involved?
If you enquire a DNO will give you a figure of 21ohms max for their side of things.
The Manx dno
Like Dave said it’s not their earthing connection, it’s upto the installer and the installer alone to determine the suitability of the electrode they install
I agree with the others saying winding a clamp on to it may have damaged their cable, they will want to take a look at that.
Reply to Max zs readings for TT in the UK Electrical Forum area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Hi All, As ever another question regarding Max ZS! I just need help reading these curves and getting my head around them. Data sheets confuse me...
Still having a discussion @ work about this…TNCS system DB/CU is a split 30ma RCD configuration,5/5 MCB’S are 60898 what Max Zs would you put in...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...