Max Zs depending on mA of RCD. Ze/Ra then above 200Ohms is not considered stable by the regs and if you enquire the DNO normally state 21 Ohms for their electrode
 
Max Zs permitted is the maximum value that the OCPD need to trip. It is not the DNO value or the 200 ohm stable value.
There is no requirement for Zs to be of a value to operate the OCPD within the required time in the event of a fault to earth. The preferred means of earth fault protection on a TT is an RCD (411.5.2) and the maximum Zs value will be in accordance with table 41.5. (411.5.3).
The maximum value whether you like it or not is 1667 ohms for a 30ma RCD and that is the value to be recorded on a cert for a 30ma RCD.
 
Last edited by a moderator:
There is no requirement for Zs to be of a value to operate the OCPD within the required time in the event of a fault to earth. The preferred means of earth fault protection on a TT is an RCD (411.5.2) and the maximum Zs value will be in accordance with table 41.5. (411.5.3).
The maximum value whether you like it or not is 1667 ohms for a 30ma RCD and that is the value to be recorded on a cert for a 30ma RCD.

Yeah that is what I said ‍♂️
 
Just realised that this thread was about Zs not Ze or Ra..
My comment about the DNO figure of <200 was Ze..
 
If it helps the NICEIC online certification gives you 200 as the autofill value to select on their forms
 
I go by what the dno insist on and the only figure that is realistically acceptable <200

Which DNO insists on less than 200?
I've never heard of this before and considering the DNO have nothing to do with a consumers own earth electrode I don't see how it's any of their business getting involved?

If you enquire a DNO will give you a figure of 21ohms max for their side of things.
 
Which DNO insists on less than 200?
I've never heard of this before and considering the DNO have nothing to do with a consumers own earth electrode I don't see how it's any of their business getting involved?

If you enquire a DNO will give you a figure of 21ohms max for their side of things.

The Manx dno
 
Like Dave said it’s not their earthing connection, it’s upto the installer and the installer alone to determine the suitability of the electrode they install
 
I agree with the others saying winding a clamp on to it may have damaged their cable, they will want to take a look at that.
 

Reply to Max zs readings for TT in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock