Discuss Max Zs TN system can’t achieve in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
51
Sorry further on from last post, TNS system, Zs can’t be achieved on final circuits, getting 1.08 Zs on a B63 0.69 but protected by 167 ohms, poor design cable runs are too long and R1+R2 proves this, now I’ve spoke with my boss about what to record in Max Zs is it 0.69 or 167 ohms as all circuits are protected by 300mA RCD, also will MCB trip on overload having not met disconnection times? Sorry this one is confusing me
 
Bradley if you are paid by your boss then he should tell you what to put down on the test sheets .
how ever you record the high test value and on the that test sheet well above max impedance value .
 
The overload part of a circuit breaker has nothing to do with the earth fault loop impedance, so yes you should still have adequate overload protection, 63 x 1.45 = 91.35 amps
This will be achieved if Ib In Iz is satisfied
 
Obviously my 0.69 for a B63 I’m not going to achieve it so in Maximum Zs permitted by BS7671 I’m not sure wether to put 0.69 for the B63 or all the circuits are protected by 300mA RCD which covers 167 ohms, I suppose either doesn’t matter? Just want to know so I’m right before asking him
[automerge]1572774522[/automerge]
The overload part of a circuit breaker has nothing to do with the earth fault loop impedance, so yes you should still have adequate overload protection, 63 x 1.45 = 91.35 amps
This will be achieved if Ib In Iz is satisfied
Thanks where’s 1.45 from?
 
Obviously my 0.69 for a B63 I’m not going to achieve it so in Maximum Zs permitted by BS7671 I’m not sure wether to put 0.69 for the B63 or all the circuits are protected by 300mA RCD which covers 167 ohms, I suppose either doesn’t matter? Just want to know so I’m right before asking him
[automerge]1572774522[/automerge]

Thanks where’s 1.45 from?
Check out section 433.1 of bs7671 co-ordination between conductor and overload device.
Typically a circuit breaker has a ‘fusing factor’ of 1.45 that is it should disconnect on overload at 1.45 it’s rating within an hour.
Nothing to do with it’s maximum‘Zs’ of the device itself
 
Check out section 433.1 of bs7671 co-ordination between conductor and overload device.
Typically a circuit breaker has a ‘fusing factor’ of 1.45 that is it should disconnect on overload at 1.45 it’s rating within an hour.
Nothing to do with it’s maximum‘Zs’ of the device itself
Top man thanks I’ll have a look
 
. a B63 will operate in approx 50 minutes @91A, thus complying with the 1.45In in 1 hour. . however, the overload current will be reduced somewhat by the increased resistance of the L and N conductors... might just be enough to make it non-compliant.
 
Last edited:
. a B63 will operate in approx 50 minutes @91A, thus complying with the 1.45In in 1 hour. . however, the overload current will be reduced somewhat by the increased Zs.. might just be enough to make it non-compliant.
How will the overload current be reduced by an increased Zs?
Overload current is just that , an overload by drawing more current than the ocpd or the conductors during non fault conditions.
Zs relates to an Earth fault between the line and cpc/ exposed conductive parts
 
Last edited:
How will the overload current be reduced by an increased Zs?
Overload current is just that , an overload
Zs relates to an Earth fault between the line and cpc/ exposed conductive parts
i put that badly. meant to say that both the L and N conductors will have a higher than expected resistance, so that in the case of an overload, the conductors will reduce it's magnitude by a small amount. just edited previous post.
 
If you measure the line to neutral loop then unless the conductors are the same size and length as the cpc you’ll probably find the line to neutral loop has a lower impedance
 
i put that badly. meant to say that both the L and N conductors will have a higher than expected resistance, so that in the case of an overload, the conductors will reduce it's magnitude by a small amount. just edited previous post.

That doesn't matter though, the requirement is only that if an overload of 1.45 times occurs it disconnects in an hour. We don't have to do anything to try to ensure that an overload achieves a particular value or disconnection time.
 
Obviously my 0.69 for a B63 I’m not going to achieve it so in Maximum Zs permitted by BS7671 I’m not sure wether to put 0.69 for the B63 or all the circuits are protected by 300mA RCD which covers 167 ohms, I suppose either doesn’t matter? Just want to know so I’m right before asking him
Anyone???
 
Agree,the Rcd will protect earth fault ,the mcb may not protect the cabling on short circuit conditions.
Due to short circuit fault conditions,with the loop impedance not complying.
 
Spoke to my boss, he’s said to put 167 ohms for RCD and all MCBs Personally I’d put 0.69 ohms and note on EICR?
What would you guys do? I’d rather know for next time, if it was TT and had 300mA RCD I’d put 167 for all MCBs but on TNS I’d put the Zs for breaker?
Thanks
 
Defo 0.69,what about changing the mcb,to accommodate Zs .
He said only put 0.69 if you can achieve it on the circuit if not rely on the Zs for the RCD which I don’t agree with
[automerge]1572800915[/automerge]
Defo 0.69,what about changing the mcb,to accommodate Zs .
Circuits are too long and feed 4/5 caravans with 16amp sockets so can’t change MCB just been poorly designed I just want to know what every one else would put rather be right as my name will be on it
 

Reply to Max Zs TN system can’t achieve in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Three questions haha 1. 160A MCCB the max Zs for this particular switch is 0.25 ohms all tested and I’m getting 0.44 ohms its a 95 SWA outgoing...
Replies
29
Views
5K
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
Local caravan site, 16/2C swa out have 3 or 4 Electric points with 2 x 16amp sockets on one circuit protected by B63 MCB now, TNS system Main RCD...
Replies
16
Views
5K
SORRY FOR LONG POST. So i have my 2391-52 multiple questions coming up on Friday 13th, ( yeh i know) and was giving some things to study over by...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock