Z

zak325

Apologies if this question sounds a bit basic but am a little confused at the mo and quite new to the game. Here goes -

I am trying to complete a NICEIC Highway Installation Certificate for a system where there is a 230 v TT supply coming into a roadside pillar into the main BS88 fused head. 6mm Meter tails then take this into a 30mA RCBO which protects the sole circuit to an accessory.

So on the certificate I have 2 circuits - 1. Supply (Distribution) and 2. Final circuit to accessory (Final)

I know there is some debate on using the 1667 ohm / 200 ohm as max Zs for the protected final circuit figure but what should I use for the max Zs of the actual supply / distribution circuit ?

If i was working on a TN system I could happily just look up the max Zs figures using Table 41.2 but am a bit stumped with this TT scenario.

Any help on this welcomed. Thanks
 
A C6 BS61009-1 RCBO protects the final circuit so max Zs (from table 41.5) I can take as 1667 ohms.

but its the gG16 BS88 supply/distribution circuit that I am trying to find the max Zs value for.
 
Maximum Values of Loop Impedance (Zs) for comparison with test readings based on 80% of maximum values above (as per Appendix 14)
Rating of Protective Device
Protective device
(MCB/ Fuse)
Disconnection
time (s)
5A
6A
10
15A
16A
20A
25A
30A
32A
40A
45A
50A
60A
63A
80A
100A
BS EN 60898 Type B
0.4 & 5
7.36
6.14
3.68
2.46
2.30
1.84
1.47
1.28
1.15
0.92
0.82
0.74
0.58
0.46
0.37
BS EN 60898 Type C
0.4 & 5
3.06
1.84
1.15
0.92
0.74
0.58
0.46
0.37
0.29
0.23
0.18
BS EN 60898 Type D
0.4 & 5
1.54
0.92
0.58
0.46
0.37
0.29
0.23
0.18
0.14
0.11
0.09
0.4
8.36
2.62
1.36
0.92
0.48
BS 1361
Cartridge Fuse
5
13.12
4.00
2.24
0.77
1.47
0.56
0.77
0.56
0.40
0.29
0.4
6.82
4.09
2.16
1.42
1.15
0.83
0.66
0.48
BS 88
HBC fuse
5
10.8
5.94
3.34
2.33
1.84
1.47
1.08
0.83
0.66
0.46
0.34
 
should i be using simple ohms law then? so for example if it is a 16A fuse then 230v/16a = 14 ohms? my max Zs would be 14 ohms?

- - - Updated - - -

sorry i posted my last whilst you posted that last message
 
3 times 16 =48 , 230 /48 = 4.7 x 0.8 =3.8

but all type b breakers is 5 times, c = 10 times, d=20 times

- - - Updated - - -

you got the green book? big 1
 
3 times the rated current of fuse it takes to blow instantly, then is why if your zs is over this it wont blow instantly in a fault...
 
it makes sense eventually... im only on year four but have done 2391 over ten weeks at a college which i think made it stick for me.... and never ending querstions..
 
You have a distribution circuit protected by a 16A BS88 fuse on a TT system so your disconnection time is one second.
The time current characteristic tables in APP3 of BGB (p300) show a table in the top right for disconnection currents for various times.
From the table a BS88-2 16A with 1s Disconnection time has a minimum current required to trip of 75A.
230V / 75A = 3.1 ohms
So max Zs of dist circuit is 3.1 ohms at 70ºC
(In BRB p248 and 72A)
 

Reply to Max Zs value for TT distribution circuit (NOT Final circuit!) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock