Hello,

I live in a house where part of the wiring dates to 1960 (exact). Now I know after ~30 years old, a rewire is advised. And at 58 years it should definitely be rewired, but it's going to be difficult to convince my parents to have the house rewired soon - as we have 5 people living here and it's going to be expensive.

What do you think is the absolute limit you can have with age of wiring? To the point it turns from strongly advised to must happen, i would like to know this to get an idea of the amount of time ticking left until it becomes too dangerous to use.

Thank you
 
I would recommend that an EICR is carried out to ascertain the state of the installation.

Only then can you tell what condition it is in. At 58 years old it could very well be in good condition and fit for another 58 years, unless DIY Bob has been at it.
 
It's hard to give a definitive answer because to some extent there isn't one really. PVC cables can last a long time, but there are many variables that can affect it. If cables are consistently used close to their limit over many years this would likely serve in reducing their lifespan, whereas cables that are hardly loaded for many years will probably last a good deal longer. Other factors include the standard of the materials used when the cable was manufactured and other influences such as environmental ones.
I have tested old aluminium cables (which I understand were around in the late sixties due to copper prices rocketing) and the results have been very good indeed. Not withstanding the fact that copper is the preferred choice of conductor.
There used to be rules of thumb (as you describe) for the life expectancy of cables, but with modern cables the intervals are probably not as prescriptive.
Your best course of action would be to get a full and thorough EICR carried out. This would give an indication as to the state of the wiring hidden in walls and under the floorboards etc. You may end up pleasantly surprised. Although you may end up aghast also!!
 
Re-wire when cables do not meet insulation resistance tests.
Re-wire when cables dis-integrate when trying to replace a light fitting or switch.
Nice to re-wire when the existing wiring does not meet the requirements for lights, sockets and other appliances.
Age of wiring is of interest but as wiring can age very differently depending on its environment, there is no must after a certain time.
 
Yep,thorough testing and a good visual inspection,done by somebody capable and trustworthy,is in order.

I know of many installations beyond the age you have mentioned,where the installed wiring tests A1,and a visual prompts no concerns.

The only exception to this,is when BG are involved...:rolleyes:
 
Hello and thank you for the replies.

I have done (sort of) a visual inspection myself. All the backboxes have 4 holes for screws rather than two. The cables are solid core, rather than stranded. The earth cable is not insulated except in the backbox itself with solid green insulation. Light switches have no earth, the new bathroom has brand new wires. Will I have to check in the loft to see if those brand new wires go all the way back to the CU? I'm worried that they could've been connected to the unearthed 1960 cable so there's no 'continuity' (if that's what you call it?). All sockets are the newer but old square MK ones.

All the cables that I have seen, just look like normal cables and aren't deteriorated, which is good.

One thing is, there's aboht 5 spurred sockets (in the 60s part of the house) to meet the demands of the appliances we use, is that a concern? Will the original cable normally handle the spurs? There's a whole other part of our house with newer wiring I'm not concerned about, but I haven't checked if it's on the same socket circuit for example. Would that be a problem?

The last inspection was in summer 2008, so I think another one is due anyway.

Thank you
 
It may be Ok, a bit of a stretch at 58 maybe but get an EICR done and then you will have a better idea as it may well be ok
 
agree with the several posts on get an EICR done. only way to see what condition the installation is in, and whether or not any remedial works are needed.
 
PS there was no requirement for earths (cpc's) on lighting circuits before the mid 1970's

Deffo an EICR and a live in rewire would not be ideal .......
Yep,my folks house was built 1963,and although wired in good quality t&e,they had clipped all the cpc's off:eek:

Rectifying that issue correctly,was still considerably easier than a rewire. Their electric underfloor heating still continues to function and pass all tests,which puts to shame some of the new systems,failing at tender ages:(
 
Yep,my folks house was built 1963,and although wired in good quality t&e,they had clipped all the cpc's off:eek:

Rectifying that issue correctly,was still considerably easier than a rewire. Their electric underfloor heating still continues to function and pass all tests,which puts to shame some of the new systems,failing at tender ages:(
underfloor heating in manchester? you'll be getting mains electrickery next. :)
 
Try not to be ageist

The system will not have standards that are now in force regards regulation changes since it was installed (that does not imply lack of safety)

If the system has not been messed up by "householder knows what he's doing" botches or stressed by heavy use,then you may even look forward to a bonus 60 years

You can also take advantage of enhanced safety features now current by upgrading to comply with these current regulations without the disruption of rewiring
 
I did a CU change last week in a bungalow built in 1968, unusually the original installation has remained unmolested with all the original bombproof [at that time] MK accessories still in place. Every circuit tested out really well, lovely old imperial stranded cable with tinned conductors, the only other thing I had to do was sleeve the CPCs at the new board and put a new main earth in, all of 600mm of 16mm cable. :)
 
Agrees with above comments. Have an EICR carried out.
I not too sure about any actual time span given for cables.
Many years ago 25 years was a given guideline for rubber cables. Some didn't get there, others went way past it!
 
I have done (sort of) a visual inspection myself. All the backboxes have 4 holes for screws rather than two. The cables are solid core, rather than stranded. The earth cable is not insulated except in the backbox itself with solid green insulation. Light switches have no earth, the new bathroom has brand new wires. Will I have to check in the loft to see if those brand new wires go all the way back to the CU? I'm worried that they could've been connected to the unearthed 1960 cable so there's no 'continuity' (

The number of holes in the backboxes has no relevance to the safety of the installation, but it will almost certainly mean they use imperial threads rather than metric.
We still commonly use solid core cables for lighting and small power in domestic installations.
The earth in a modern T&E cable is not insulated and would only be sleeved where the cable is stripped for terminations, the only difference is that we use green and yellow stripes now.

Yes a lack of earth in the lighting circuits is a safety concern and should be rectified when possible. Be wary of people advising that an RCD and a yellow sticker are a suitable alternative, they are not!
 

Reply to Maximum age of wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
853
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
605
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
816
HI I am not a professional electrician but have cabled all my houses since starting to build them 30 years ago. I know a dangerously small...
Replies
5
Views
595
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock