can someone please help me with this question

There is a 40A BS88 fuse, protecting a 10mm cable with a 4mm Earth, it is wired to Reference method C, supply is TNS and it is protected by a 30mA RCD. What is the maximum length the cable can be?

(thats all the info i have! I haven't been to collage for couple of years now and cant remember how to do it )
 
find max zs then deduct ze wich will leave r1+r2 rearange formula to make length the subject:

r=mva x length/1000

so

l=r x 1000/ mva

that should work
 
Last edited by a moderator:
thanks for that mate, but i dont know if it swa. how would i work it out? is it by doing the volt drop per meter?
Thanks,
Vidz
 
is it

45(amps) x 4.4 x 45(meters) / 1000 = 7.92 (which is just under the maximum 4% voltdrop)

is this correct?

sorry guys but i'm a bit rusty lol

Thanks
 
Last edited by a moderator:
Dont have regs to hand but guessing something like :

Ze = 0.8
Zs max for 40a bs88 = 1.35 deduct ze zs leaves r1+r2
1.35 - 0.8 - r1+r2 of 0.55
so r1+r2 = mva (for 10mm.4mm) x length (not known) / 1000
0.55 = 6.44 x L / 1000
rearrange to length = r1+r2 x 1000 / mva for 10mm.4mm

L = R X 1000/ MVA
L = 0.55 X 1000/ 6.44 = 85 METERS

thats what the max length for zs comes out at although a volt drop calc would need to be done also
 
Last edited by a moderator:
values of resistence table 9a osg.



that would give the max cable length to meet earth loop value but would be too long to meet allowed vd
 
Last edited by a moderator:
Maximum length according to volt drop on t&e cable carrying the full nominal current rating of the Overcurrent Protective Device at a nominal voltage of 230v assuming cables are not grouped.

1.0mm / 6A : 26m
1.5mm / 6A : 39m
2.5mm / 16A : 39m
2.5mm / 20A : 31m
4.0mm / 20A : 52m
4.0mm / 25A : 41m
6.0mm / 32A : 49m
10.0mm / 40A : 65m
16.0mm / 60A : 68m
 
just looked it up and its same formula from a simmilar worked example used in "practical guide to testing book"

zmax for fuse - the ze = R1+ R2

R1+R2 x 1000/ mva = length (Rearranged from R= mva x length/ 1000)



Cant see any other way of calculating without knowing the vd or the length.
Sintra gives a value of 10.0mm / 40A : 65m but need to see how he calculated it
 
Last edited by a moderator:
(mV/A/M) * Ib * L / 1000 = VD

Rearanged.

VD / Ib / (mV/A/M) * 1000 = L

Max Vd = 11.5 V

Ib = 40A

mV/A/M for 10mm T&E = 4.4

11.5/40/4.4*1000 = 65.34M rounded down to 65M
 
VOLTAGE DROP

The maximum permitted volt drop measured from the incoming supply is 3% for lighting circuits and 5% for all other circuits. p358

230v x 3% = 6.9v

230v x 5% = 11.5v
 
Thought I was going mad for a minute and somebody had removed my post.

This question was also posted HERE which is where I replied to it.

Ring circuit

4 x (Max Zs - Ze) ÷ ((R"1 + R"2) x Cr)


Radial

(Max Zs - Ze) ÷ ((R"1 + R"2) x Cr)


R"1 + R"2 = Resistance per meter of Line & Cpc conductors
Cr = Correction factor for conductor operating temp of 70°C

So lets assume your Ze is 0.8 (max for TN-S). The max Zs for a 40A BS88 fuse is 1.35Ω and the R"1 + R"2 of 10/4.0mm² cable is 6.44mΩ per meter.

The calculation would be:

(1.35 - 0.8) ÷ ((6.44/1000) * 1.2) = 71m

However most maximum circuit lengths are limited by Voltage Drop and the voltage drop of 71m of 10mm² cable carrying 40A is 12.5V which exceeds the 11.5V (5%) maximum VD for a power circuit.

VD = mV/A/m x Length x Current
VD = (4.4/1000) x 71 x 40 = 12.5V


So you would need to work out the max length for Voltage Drop

Ring

4 x (Max VD x 1000) ÷ (mV/A/m x Current)


Radial

(Max VD x 1000) ÷ (mV/A/m x Current)


So for your circuit the calculation for VD would be

(11.5 x 1000) ÷ (4.4 x 40) = 65m
 
Last edited by a moderator:

Reply to Maximum Cable Length?? in the Australia area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock