ithink its about 50m end to end but that's just a guesstimate.
 
the OSG has a table in there giving maxium cable lengths for cable size but as I haven't got mine with me can tell you which one, sure if one of the other lads are following this thread they can give you the table reference
 
if the area covered is 100m2 then does that mean that the cable can be 40 meters long end to end (ie going around a square room that is 10x10m meaning it would cover 40m end to end?

subject to all other criteria being met
 
in a 10X10 meter square what about the drops or rises.....if the rooms got a 5 meter celing hight and your drop is from there then how big would your ring main be...
its all about cable resistance and what protection you have and the temperature and the insulation around the cable.....
if i were you id look into some cable calcs....they are a wonder to behold..
 
I atually searched and found a reference earlier which said something like 98m for 2.5 and 178m for 4.0

this i think must be the maximum for each and could be lower depending on other influences
 
what about the drops/rises to sockets. as vito says, have to meet Zs less than 1.2 for a 32A type MCB, so knowing Ze and the resistance of R1 and R2 per 100m each, you can work it out
 
in a 10X10 meter square what about the drops or rises.....if the rooms got a 5 meter celing hight and your drop is from there then how big would your ring main be...
its all about cable resistance and what protection you have and the temperature and the insulation around the cable.....
if i were you id look into some cable calcs....they are a wonder to behold..

You are right but have forgot more than i now know!! been working easy for 10 years and need to refresh my electrical installation theory.

anyway thanks for any help from all
 
I think its a bit of no can answer question
As Lenny said,voltage drop is the main factor because of the limits now in force
Voltage drop is dependant on not only the length but the load and the cable resistivity
and the cable size

If any of these are changed ,the answer will also change
We can follow the general guidance for 100meters square and it would probably be within limits.but as pointed out by others even then it could be outside that limit
Also the type of load that affects voltage drop limits,if there are lights in circuit,there is less to play with

Tricky question I reckon
 
table 9a osg page 166

2.5 cable with cpc 1.5 has resistance of 0.01951 ohms per metre

x by 100 metres = 1.951 ohms

now max zs for 32 A mcb type b is 1.16 ohms.

a ring has double the csa therefore if u divide it by 2 you get 0.9755 ohms

ie 50 metres out on a ring cct and 50 metres back.

this does not take into account any other losses, so answering your question, the rule of thumb is 100m squared, give or take a few metres!? as long as the max zs is within limits, it should not matter.

hope this helps and that im not talking poop?!
 
Its a funny job which i have been left with and can only give vague details as i have only vague details thus far!

I know this maybe a tuff question but i will tell you all i know and lets see where this goes

the circuit i have to install is on an industrial site and compromises of 4 switched fuse spurs taking 5 amp each and the ring will be about 130m!!

so do you think 4.0mm with a 20amp breaker is my going to be the only option that will comply!

and again thx for any help
 
Last edited by a moderator:
i.d go with a 32A MCB as a 20A is on its limit at 4 x 5A. Volt drop and cable resistance are the 2 factors you have to watch for. Find these values per 100m and per amp and you've answerede your query
 

Reply to Maximum cable length in the Australia area at ElectriciansForums.net

Similar Threads

This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
864
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
615
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Replies
4
Views
536
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
783
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock