I'm always in a dilemma with regards max demand. Often you work it out and it's higher than the the 80A or 60A cut out fuse. However, you know that in reality it is absolutely fine.

I have thought about this in the past when installing electric showers. Now with EVCP's as well it's making me think a bit harder!

The DNO around here will only allow an 80A fuse if meter is inside. Let's give an example of a standard house.

Shower 40A
Cooker 32A
Sockets 32A
Sockets 32A
Garage 16A
Boiler 16A
Lights 6A
Lights 6A

With the osg diversity (which I rarely use for total demand of house hold), you nearly always get >80A. With the 40% rule in the above example you get 72A which is more realistic, but still leaves no room for a 7.4kW EVCP.

Would you fit one anyway, knowing it will be ok?
What would you guys do realistically?
@Gavin John Hyde , you must come across this lots. I realise there is the CT clamp option, but in this standard example is it really necessary?
 
I'll take a guess

If it's strictly off-peak it's ok.

It mostly is but not strictly off-peak so you'll need some type of interlock or throttling of the car charging

Don't see any way round it
 
I'm always in a dilemma with regards max demand. Often you work it out and it's higher than the the 80A or 60A cut out fuse. However, you know that in reality it is absolutely fine.

I have thought about this in the past when installing electric showers. Now with EVCP's as well it's making me think a bit harder!

The DNO around here will only allow an 80A fuse if meter is inside. Let's give an example of a standard house.

Shower 40A
Cooker 32A
Sockets 32A
Sockets 32A
Garage 16A
Boiler 16A
Lights 6A
Lights 6A

With the osg diversity (which I rarely use for total demand of house hold), you nearly always get >80A. With the 40% rule in the above example you get 72A which is more realistic, but still leaves no room for a 7.4kW EVCP.

Would you fit one anyway, knowing it will be ok?
What would you guys do realistically?
@Gavin John Hyde , you must come across this lots. I realise there is the CT clamp option, but in this standard example is it really necessary?
With the new DNO form you are 90% of time going to have to submit your ema form pre install anyway. WPD will send you a pre works letter or email saying go ahead or we are changing cut out.
In this scenario i include covering letter and images of the mcbs. The planners like this and I explain that calculated MD vs real life MD is completely different. They get this and normally say go ahead if its and 80+ amp supply. My experience is DNO only get twitchy if its a 60a or looped supply.
 
With the new DNO form you are 90% of time going to have to submit your ema form pre install anyway. WPD will send you a pre works letter or email saying go ahead or we are changing cut out.
In this scenario i include covering letter and images of the mcbs. The planners like this and I explain that calculated MD vs real life MD is completely different. They get this and normally say go ahead if its and 80+ amp supply. My experience is DNO only get twitchy if its a 60a or looped supply.
When talking to the planners at WPD they said in calculating MD they typically ignore lighting unless it has significant number of.fittings. when you think about it though it makes sense as so much stuff now is ac to dc via adaptors. And lights are led. My new oven uses a 13amp plug albeit.coming off a 10mm/40amp circuit... So the md calculations are not very reflective of real life
 
How do you calculate demand in the UK

100% immersion
100% shower
100% water heater
100% evcp
Sockets 100% largest appliance +40% of each other large appliance
Cooker 10A +30% remainder

Add them all up and ignore lighting, figure for other appliances seems too high at 40%

Calculating off mcbs seems like a waste of time , figure could be way off
 
Some evcp,s have current transformers and you can set the cut out fuse so that its never exceeded ,mcbs ratings are useless as they don’t always reflect design current .
 

Reply to Maximum demand and EVCP's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hi all, I have a regular client who has asked for a battery back up system to be installed at their home. They live in a rural location on a...
Replies
2
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
A couple of questions for you. The electrician that rewired our house ran a 10mm2 SWA to our outbuilding. The total length of the cable is about...
Replies
17
Views
4K
Hi. Could you please advise on whether 63A RCDs are acceptable when the service fuse is 80A? I have the following setup: 80A service fuse - 100A...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock