EddieB

-
Arms
Reaction score
27
Table 41.3 gives the maximum earth loop impedance on a type B 32a breaker to 60898 as 1.44 ohms, the testing schedule on the domestic cert asks maximum permissble loop impedance, in the test and inspect notes I seem to remember that you are required to write the full 1.44 but I'm sure that you allow for 80% due to fault condition temprature?? bringing it down to 1.15. Answers on a virtual postcard please
 
It says on the cert MAX Zs.

This is before any correction is made.

Does seem a a bit daft as i would have thought the corrected value would make more sense as its a tad lower.
 
testing power and light circuits..
if i have a typeC 20amp RCBO with 4mm cable feeding a radial power cicuit what sort of testing am i doing to get fault loop impedance
 
Table 41.3 gives the maximum earth loop impedance on a type B 32a breaker to 60898 as 1.44 ohms, the testing schedule on the domestic cert asks maximum permissble loop impedance, in the test and inspect notes I seem to remember that you are required to write the full 1.44 but I'm sure that you allow for 80% due to fault condition temprature?? bringing it down to 1.15. Answers on a virtual postcard please
It depends on who's schedules you are using.
The NICEIC ones require the value from BS7671, whereas I believe that with ELECSA it is either the full or the 80%.
Of course, with the IET ones it's neither.
 
no, you are right. LFLI test is a live test. ( unless you want to calculate it, as malcolm.)
 

Reply to Maximum earth loop impedance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi there, I’m just hoping someone could clear something up for me at all. I’m just working my way through some test questions and I’ve come across...
Replies
24
Views
3K
Morning all. So just trying to refresh my grey matter but having a biff moment. Earth fault loop impedance with circuits protected by BS EN60898...
Replies
4
Views
2K
To keep your trainee brains in tip top condition during lockdown, here's a few quiz questions.... 1) A fault report is 'Circuit breaker keeps...
Replies
4
Views
2K
Iv been given the scenario: 6 circuit earth fault loop impedance values were recorded. Each circuit has type B cb. referring to the maximum...
Replies
25
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock