H

harry olee

In order to meet current regulation the maximum meter tail length should be no more than 3M and if over a 100amp fused switch should be fitted - is that correct.
(This guidline is not in the iet on-site guide except that this maybe specified by the distributor)

521.10.1 mentions that the tails should be insulated and sheathed or insulated and enclosed within containment. What should the composition of the sheathing be, 25mm cable comes with a grey plastic sheath.
eg:
BASEC approved PVC insulated and sheathed, single core stranded cable to BS6004 Table7. Commonly used as meter tails for connecting consumer units to the electricity meter.

This cable does not require enclosure - is that correct.
 
If over 3m in length then a fuse switch is generally required. Tail lengths can then be extended as required. ...Think about tail lengths required in apartment blocks etc, they are going to be well in excess of 3m aren't they!!!
 
In order to meet current regulation the maximum meter tail length should be no more than 3M and if over a 100amp fused switch should be fitted - is that correct. There is no definite length stipulated in either the Regs, or the OSG, the OSG as you say advises that you ask the DNO and if you exceed their recommended distance then yes you have to supply protection for the tails, normally as you say a Switch Fuse.
It may also need RCD protection as well depending on your erection methods and type of earthing system
(This guidline is not in the iet on-site guide except that this maybe specified by the distributor)

521.10.1 mentions that the tails should be insulated and sheathed or insulated and enclosed within containment. What should the composition of the sheathing be, 25mm cable comes with a grey plastic sheath.The "Sheath" would be PVC the same as Twin & Earth
eg:
BASEC approved PVC insulated and sheathed, single core stranded cable to BS6004 Table7. Commonly used as meter tails for connecting consumer units to the electricity meter.

This cable does not require enclosure - is that correct. Correct


...................................
 

Reply to maximum meter tail length and composition in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi, Just had a new Smart Meter fitted yesterday along with isolator. The chaps installing the SMART meter used 16mm tails from the main DNO fuse...
Replies
16
Views
8K
...and why would I want to do that ? Well, I'm faced with a real botch job of a consumer unit. Essentially this is a "new" consumer unit only put...
Replies
21
Views
9K
Hi everyone, Bought some Flexi meter tailes from a supplier today , Am I going crazy or that I marked up incorrect . The Flexi tiles I’m used to...
Replies
10
Views
5K
I’m rewiring a massive house and there’s a feed to a c.u in the old black rubber cable that needs replacing. I know that Meter tails follow the...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock