DanBrown

H i Guys!
Ive already asked for a maximum zs for a bs 88 20 amp fuse!,
but any idea about a bs 88 fuse rated at 63 amps.
I can only see one table and that suggests 5 seconds disconnection.

It comes off a bussbar to a fused isolator and the to a ventilation heater. Am i right in saying 5 seconds is too high, or because it comes from the bussbar to a fused isolator it is classed as a distribution circuit.
Thanks anyway
 
Dan,

If you look at BS7671-2008 you will see from regulation 411.3.2.3 that a 5 second disconnection time is allowed.

The maximum Zs for the 63 amp BS 88-2.2 is 0.82 ohms as per table 41.4

You probably worked this out already but here it is anyway.

BR3
 

Reply to Maximum Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock