I don’t like that set up at all, 6mm cable should be protected by 32A protective device especially when you consider insulation factors, so from the utility meter what csa of tails/cable is selected 6mm? And what size supply cut out fuse is there? If it’s 60A needs to be 16mm if it’s 80/100A needs to be 25mm in my opinion. That diagram isn’t a British one is it?

Tails wouldn't necessarily need upgrading to 25mm.
 
I don’t like that set up at all, 6mm cable should be protected by 32A protective device especially when you consider insulation factors, so from the utility meter what csa of tails/cable is selected 6mm? And what size supply cut out fuse is there? If it’s 60A needs to be 16mm if it’s 80/100A needs to be 25mm in my opinion. That diagram isn’t a British one is it?

6mm on a 40a mcb is what virtually everyone uses in my country. note that we don't use thermal insulation and its also up to local code as long as there isn't a long distance.

I know that its debatable whether to use a 10mm or a 6mm on a 40mcb but things are what they are and most likely a 6mm is used due to cost and ease of installation. I agree with you that it would be best to opt for the 10mm just to be safe because while a 6mm is in theory enough other things can effect performance - but its not up to me to decide.

From the utility meter its also 6mm and the supply is capped at 40a. Don't know about the fuse for this particular meter because none of this is already installed.

the diagram is not British
 
Looking at your diagram do you mean 300mA/100mA instead of 300ms/100ms for the RCD as you also say delay and no-delay?

A 100mA RCD without delay is not considered acceptable here for personnel protection against shock, it has to be 30mA (or less no-delay). Really you would be better with three RCBO that each provide the 30mA protection if you have concerns about total leakage being too high for a 30mA incomer.
 
Looking at your diagram do you mean 300mA/100mA instead of 300ms/100ms for the RCD as you also say delay and no-delay?

A 100mA RCD without delay is not considered acceptable here for personnel protection against shock, it has to be 30mA (or less no-delay). Really you would be better with three RCBO that each provide the 30mA protection if you have concerns about total leakage being too high for a 30mA incomer.
actually the diagram was just a quick sketch without being too technically detailed.

As you know when rcd's are used in succession such as in this case one must take into account discrimination. the 100ms (<= 100ms) is the tripping time of a standard rcd which is meant to trigger the moment theirs an earth leak without any delays

The 300ms is the delay for the upstream rcd.

The above just means that the downstream RCD will trigger first, followed by the upstream RCD (if leakage is still present)

RCBO's are cost prohibitive unfortunately
 
actually the diagram was just a quick sketch without being too technically detailed.

As you know when rcd's are used in succession such as in this case one must take into account discrimination. the 100ms (<= 100ms) is the tripping time of a standard rcd which is meant to trigger the moment theirs an earth leak without any delays

The 300ms is the delay for the upstream rcd.

The above just means that the downstream RCD will trigger first, followed by the upstream RCD (if leakage is still present)
For selectivity you need both a difference in current threshold and delay. The first so a small slowly rising fault trips the downstream one first, the delay so a hard fault (which exceeds both currents) is cleared by the downstream one before the upstream one decides to act.

RCBO's are cost prohibitive unfortunately
What is your definition of prohibitive? You can get RCBO for £17+VAT each in the UK, for example:
https://thomaselectricaldistributors.co.uk/product/fusebox-mini-rcbo-double-pole-type-a/

If you only have 3 or so final circuits there and delete the cost of an incomer RCD due to the RCBOs providing that, it is not such a big coast difference for higher reliability.
 

Reply to MCB as a Main Switch in Garage Panel? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
707
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
782
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock