jamesBoater

6 amp BS EN 60898 .....6ka being the maximum fault current the device can handle, although the device may no longer work after that. The 3 underneath this being the fault current (ka) the device can handle without damaging it and then being able to be reset.

I have been told 2 different reasons that the 3 appears under the 6ka so would just like to see what anyone else has on this.


Thanks James.
 
The 3 being what fault current the device will safely interrupt without internal damage to it. (Was taught this today in college by a teacher of 35 years in the trade)

The 3 having no relevance to RSCC with the device.
 
I'm interested in what your tutor would reply to this:-

If you have a prospective fault current of 7.5kA once established by testing, why would you not change the MCB's to a 10kA ratting?

How can he test the MCB after a fault occurred and what fault current flowed at the time?
 
If you have an upstream device that has higher than fault current rating then mcbs etc downstream dont need to meet the kA rating of the fault current but if you have the option to its good practice to do so and fit a higher kA rating.

You need to seek manufacturers advice to the actual tolerances against tabulated but any device that has had a fault current exceeding it kA rating should be replaced but has anyone ever bothered ... especially domestic when numerous faults may have occured on any given breaker that may have exceeded it kA rating.
 
Another MCB i looked at (10ka) also has a 3 under it!

As I understand it, Its the class rating of the device,, it can be 1,2 or 3 ,3 giving the least let through energy or I2t on a fault (the best)
If you look at a manufacturers data sheet it gives you the values which can then be used to design your installation.

Here you go .. have a look on page 12 of this
http://energy.te.com/getDocument.aspx?PRD_ID=3628
 
Last edited by a moderator:

Reply to MCB short circuit capacity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
763
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Hello, I have an old 16A Wylex SK type B plug-in breaker in the fuse box in my garage which keeps tripping, and every time (and only at that time)...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock