Discuss MCB sizing for parallel cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

podger

-
Reaction score
0
Addition to old installation - routing through trunking to supply a sub-board with two 6mm SY cables.
However, I can't find any info on sizing of MCB to maximum Zs for parallel cables - -?
Seems to me the problem could be using calculated Zs for the two in parallel as in the event of a fault occurring at far end in one cable only - you're only dealing with the Zs of that cable to meet the MCBs overcurrent requirements - - (i.e. this would be double the Zs of the two in parallel)
So it's ok doubling current carrying capactiy for the two in parallel, but it seems using parallel Zs to determine suitable MCB could be bad practic here. In which case I'm goosed!
Can anyone shine a light ?
 
Why? Zs is the same as long as the parallel regs are met, eg same route, same length, same size etc.

You could say the same about the current capacity
 

Reply to MCB sizing for parallel cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hello I have two new appliances Electric oven rated at 3.95 KW Induction hob rated at 7.2 KW total of 11.15 KW Currently it is on its own...
Replies
17
Views
3K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock