Discuss megger 1552 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
R
Ross Trician
Hello all, I am after some advice,
I have just bought a megger 1552 tester. I was "practicing" with it today as I am a novice when it come to inspection and testing. I found the instruction manual a bit naff. I was trying to do a Zs/earth fault loop impedance on a radial circuit and the meter kept saying "trip" the way I interprited using the meter is it can use a 2 lead rather than a 3 lead test but shows trip. if I also put the black lead to neutral it gives a reading.
could someone please give me some clarity on the method or what I am doing wrong.
Any help would be appreciated.
Ross.
presumably you are on 'no trip loop'
on the side of the meter, there is a black hole at the bottom with 'no trip loop' written on it.
it does what it says on the tin!
if you are set to 'no trip loop' for EFLI or PFC then you must puit your black lead in the no trip loop hole and connect it to the neutral of the circuit you are measuring
you will find as well, if you were measuring Ze using no trip loop you DONT disconnect the main earth!
its just the way it is......have fun now
and test safely!;)
Thanks for the quick reply Shakey.
I would of thought the instructions that come with the tester would be a bit beter than what they are. I have been an electrician for a good few years but not familiar with the inspection and testing side of things. do you have experience with the megger meter? if so whats your opinions etc of it,,
Cheers Ross.
yeah, got lots of them, very very experienced with the meter
simple to use, but a bit slow on the no-trip functions
but like you have discovered, the manual is useless, and i badgered Megger into supllying me with the plug top lead with the three connectors on (so you can do the ring cross connects) for free
it hacks me off the way they want you to buy extras
bought a few PAT testers off thwem, and the 'extras' were going to be over 150 quid per meter on top!!!
I say 'were' cause bulk buying gives you a bit of leverage;);)
Hi, I have a megger 1552 that gives completely different results when
measuring "Hi" & "no trip" impedance values. The Hi value seems to give the most accurate result (compared to another meter) while the no trip value always seems to be a lot higher. It seems to only happen when
trying to test at a particular premises containing 21 flats with 3 phase
incomming supply. Ze (hi) = 0.25 whilst Ze (no trip) = 2.85.
I have had the unit checked by a calibration lab but they cannot find any
faults with the meter. Could this be caused by high voltage fluctuations/ noise in the circuits?
Thanks Wayne
You will find that any test meter that has a no trip function will give different readings due to the nature of how it carries out the test without tripping.
check for the dvd that came with the tester, its with the calibration cert in the top of the megger box. Shows how to do all the tests. very helpful.
If your doing a zs test why not use the plug attachment that comes with the tester rather than the leads if its a radial socket circuit hth cheers
I've only ever used the Hi setting and 2 leads for the measurement of Ze. Is this wrong?
Have a look at the following links for some instruction
[ame]http://www.youtube.com/watch?v=PniIhehMNf8[/ame]
[ame]http://www.youtube.com/watch?v=p_Blib9qUO0[/ame]
with the 1552 on no trip Zs test you must use 3 leads or the plug-top lead
Reply to megger 1552 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Hi I've got a megger mft 1720 that I was hoping any one can shed any light on When performing continuity tests (even when nulling the leads)...
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Just thinking about selling MFT's and single test equipment. The idea being I buy stuff from Ebay and sell it on ebay, which I am doing at the...