Can anybody tell me,what’s the difference worrying about short circuit conditions on Zs readings that don’t comply,but are protected by a rcbo,difference I’m after are on TN & TT.
The Zs would be still high on a tt system like a tn system,when circuit does not comply, maybe the cable would not comply on short circuit calculations,on both.
 
Can anybody tell me,what’s the difference worrying about short circuit conditions on Zs readings that don’t comply,but are protected by a rcbo,difference I’m after are on TN & TT.
The Zs would be still high on a tt system like a tn system,when circuit does not comply, maybe the cable would not comply on short circuit calculations,on both.
Hi cliffed. Please could you clarify your question? When you say short circuit calculations, do you mean the adiabatic equation applied to a L-N fault?
 
Are you specifically concerned about a L-N short circuit? If so, Zs is irrelevant, as is the RCD element of the protective device. You need to measure the L-N loop impedance, which even for TT should be low enough for the MCB element to adequately protect the cable. If it's not good enough, then it's the usual method for fixing it... upgrade the cables to drop the loop impedance or drop the RCBO rating so the circuit loop impedance is lower than the maximum Zs for the device.
 
If the Zs is high the Pscc would be low, so would the cable be @ risk concerning the short circuit fault condition

Zs is the earth fault loop impedance so the PEFC will be low, this is where the RCD element comes in, but if you're talking about a L-N short, then you'll need to check the L-N loop impedance which is what governs PSCC. Like I said, I suspect you'll find the L-N loop impedance is low and thus PSCC is high, so the MCB element will work as expected in the event of an L-N short.
 
If the Zs is high the Pscc would be low, so would the cable be @ risk concerning the short circuit fault condition
Something to bear in mind is that the PSCC would be highest at the origin of the circuit. The further downsteam of the OCPD the L-N fault is, the greater the impedence, therefore the lower the PSCC.

We use the adiabatic equation to ensure the cables don't fry in the event of a short circuit, ie that the let through energy (I²t) is low enough. For BS60898 MBCs, the let through energy increases as fault current increases (see below attachment). Worst case is at the origin of the circuit, so use the PSCC from here for your calculation.
[automerge]1577014918[/automerge]
 

Attachments

  • letthroughenergyhager.pdf
    98 KB · Views: 8

Reply to Merry Christmas in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
764
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock