newfutile

-
Arms
Reaction score
111
Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:  American Electrical Advice Forum

We have had 2 metal steps installed to cover main supply cables (out to flats) from a Ryefield .
when measured IR from MET to steps i got 0.091 MegOhms.

The usual calculations are for when a 30 ma RCD is protecting (which is not the case here)

91 Kohm is above the usual value of 23 Kohm I usually use (10ma).

Should these be bonded to earth?
 
Reaction score
31
I wouldn't earth it. As you say using the equations the maximum current that flows through the body is < than 10mA.

Using the formula from GN8:

You don't have permission to view attachments. Attachments are hidden.

rearranged to:
You don't have permission to view attachments. Attachments are hidden.


I get 2.5mA when taking ZT as 1000ohms as suggested in the guidance.

Are there any other earthed parts within touching distance? GN 8 states "Consequently, for a conductive part to be able to introduce a potential to a person (or livestock) in contact with the potential of any of the conductive parts, that part should be accessible to such a person (or livestock)." I assume this would also apply to your situation.

(I am referencing the 17th ed amd 2 of guidance note 8)
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.

Reply to Metal steps secured to concrete (bonding) in the Electrical Forum area at ElectriciansForums.net

Similar Threads

newfutile
In a communal electric intake room for flats (meter room) there is lots of bonded trunking and tray, also the metal door frames were found to have extraneous parts linked to earth , these have now been bonded. They have now fitted a metal floor , i have not conducted a IR test to earth as yet...
Replies
1
Views
120
pc1966
P
Mark42
I'm a bit out of touch re 18th edition. Is it really necessary to fit loads of additional metal saddles inside trunking when it's only 400mm above the concrete ground floor of a sports hall? All the stuff about premature collapse makes sense, but where, in this case, if the cable going to...
Replies
3
Views
249
pc1966
P
Marvo
I see in the UK that RCBO's are more becoming a standard installation now. I might be missing something obvious here but I've been wondering why are the commonly used RCBO's rated to 30mA leakage current when they're only protecting a single final circuit. Surely 30mA leakage on a normal...
Replies
23
Views
760
LastManOnline
L
Rockingit
Industrial refit and we’ve screwed a bunch of metal clad 13’s onto walls which are corrugated metal sheet using self tappers. Just come to do dead tests and realised that r2 is about half the value of r1 and rn - the sheet is acting a conductor. Sup Bond the sheet or not? The same walls...
Replies
11
Views
436
cliffed
C
I
Advice required from the more experienced and knowledgeable. Has anyone installed power to one of these prefab concrete garages with a steel roof structure, steel clamps (on concrete panels), steel door mechanism and damp concrete floor? My conundrum is that I intend on upgrading the current...
Replies
2
Views
268
ijmac021
I

Electrical News from Electricians Forums and Friends

E
  • Article
Want to become a qualified electrician? Look carefully at the training courses on offer to avoid wasting time and money, is the advice in a new campaign from electrical industry body The Electrotechnical Skills Partnership (TESP). With thousands of searches each year on terms such as...
Replies
49
Views
6K
Marty92
Dan
  • Article
You can now link your account with social media by going to the following page. https://www.electriciansforums.net/account/connected-accounts/ We had this feature some time ago but I removed it when Facebook was found to be selling the data they collected without informing the users of what...
Replies
0
Views
2K
Dan
Dan
  • Article
There was a dodgy advert, typical clickbait, showing "how to save 90% on your electricity bill" which was not the case and it was actually showing some dangerous wiring tactics. Read the actual threads here:- What should be the code for this - C2 or C3 -...
Replies
37
Views
8K
Jurassic Sparks
Jurassic Sparks
James
  • Article
The Go Plus hot tub is being recalled because you could get electrocuted taking a dip, according to press releases from the Chartered Trading Standards Institute (CTSI). An Amazon spokesperson said: "Safety is a top priority at Amazon. "We require all products offered in our store to comply...
Replies
6
Views
3K
Dave Appleby
D
Dan
  • Article
Posted on behalf of @CKI:C.K-Tools Carl Kammerling International Ltd, also known to as ‘CKI’, are the company behind the C.K Tools brand. Founded in Germany in 1904 and with roots stretching back to 1790, we provide a wide range of hand tools, tool storage, power tool accessories and...
Replies
2
Views
4K
telectrix
telectrix

Search Forum

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Top