Arms
Reaction score
119
Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

We have had 2 metal steps installed to cover main supply cables (out to flats) from a Ryefield .
when measured IR from MET to steps i got 0.091 MegOhms.

The usual calculations are for when a 30 ma RCD is protecting (which is not the case here)

91 Kohm is above the usual value of 23 Kohm I usually use (10ma).

Should these be bonded to earth?
 

Aaron b

Trainee
Reaction score
44
I wouldn't earth it. As you say using the equations the maximum current that flows through the body is < than 10mA.

Using the formula from GN8:

Metal steps secured to concrete (bonding) 1637827866097 - EletriciansForums.net
rearranged to:
Metal steps secured to concrete (bonding) 1637829024815 - EletriciansForums.net

I get 2.5mA when taking ZT as 1000ohms as suggested in the guidance.

Are there any other earthed parts within touching distance? GN 8 states "Consequently, for a conductive part to be able to introduce a potential to a person (or livestock) in contact with the potential of any of the conductive parts, that part should be accessible to such a person (or livestock)." I assume this would also apply to your situation.

(I am referencing the 17th ed amd 2 of guidance note 8)
 

Reply to Metal steps secured to concrete (bonding) in the Electrical Forum area at ElectriciansForums.net

Similar Threads

In a communal electric intake room for flats (meter room) there is lots of bonded trunking and tray, also the metal door frames were found to have...
Replies
1
Views
154
Advice required from the more experienced and knowledgeable. Has anyone installed power to one of these prefab concrete garages with a steel roof...
Replies
2
Views
337
Hi all, quick question, I have come across a 230V control circuit supplied from an Isolation Transformer. The controls are located within a metal...
Replies
3
Views
289
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
2K
I see in the UK that RCBO's are more becoming a standard installation now. I might be missing something obvious here but I've been wondering why...
Replies
23
Views
1K

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Top