Hi everyone, I am not an electrician and have joined this forum for some help. Here is some background information to my incident:-

Background

House Built 1985
Took ownership December 1999
Electricity meter replaced by electricity supplier 12 January 2004
Consumer unit upgraded 16 January 2008
Current Incident March/April 2017

Incident

During March 2017 I noticed a thud in the lounge on right hand wall and investigated and could not find the cause

The thud or popping sound continued four or five times daily until 2 April 2017 when I investigated further. The electricity meter box was open and I looked inside and noticed the meter tails had a sooty deposit and was arcing.

I contacted my electrician who told me to switch off the power at the consumer unit and he came out immediately and made everything safe.

He noticed that the meter tails were of the wrong size being16.0mm² twin and earth cable old colour conductors of red and black (current rating 70Amps). Possibly original installation as the only work I had done is detailed above.

I agreed that the meter tails be changed to correct specification of 25.0mm² double insulated tails (current rating 110Amps) with 16.0mm² earth (current rating 74Amps).
This work was completed on 4 April 2017

Conclusion

There was an electrical storm early March 2017 and I noticed shortly afterwards that my AV amplifier stopped working due to a short burn fuse blowing. I can only assume that the electrical storm caused a power surge sufficient to not blow the main fuse on the incoming supply at the consumer unit but sufficient to cause heating and arcing of the twin and earth cable which had a current rating of 74Amps.
Is this feasible?
 
Was the sooty residue at the connections to the meter, which wire was it in your case black or red, if so how far up the wire did the scorching extend? Any idea what size the DNO's fuse is?
 
Was the sooty residue at the connections to the meter, which wire was it in your case black or red, if so how far up the wire did the scorching extend? Any idea what size the DNO's fuse is?
The sooty residue was not at the meter connections but some 10 inches down from the meter where the red and black wires were arcing/shorting, burning the insulations and sheath. I do not know the DNO fuse but have assumed it to be 100Amp.
 
As above it sound to me during the meter change or consumer unit upgrade the connections were left loose , which coarse the burning, not the power surge ,The fuse in your amp could of blown for many reasons , the electrical storm being one of them

Edit
OK Sam with that additional information it may not of been a loose connection but a damaged cable
 
Its a loose connection 100%... if it was a lighting strike which filtered into the Electrical system it would do more damage than just blow a fuse in an amplifier and this. also if it was a demand issue i.e you were taking more current than the cable could take, then I would expect to see this thermal damage in more place, along the cable either end of the cable connection at the meter and main switch would be equal susceptible to this damage Live and neutral as well, but if its in one place like this then its a loose connection.
 
Where the 16mm cables were damaged, were they touching each other or anything else? Either they were damaged by heat alone, or had their insulation damaged (by something...) which allowed arcing and further burning damage. Does that fit what you saw? Moral of story - always take a pic :)
 
Where the 16mm cables were damaged, were they touching each other or anything else? Either they were damaged by heat alone, or had their insulation damaged (by something...) which allowed arcing and further burning damage. Does that fit what you saw? Moral of story - always take a pic :)
Where the 16mm cables were damaged they were touching each other and glowing red. There was nothing rough enough nearby that could have caused damage to the cables through abrasion.
I was too s**t scared when I saw what was happening that a photo was the last thing on my mind.
 
Whilst 16mm may be rated at 74Amps it will not overheat and fail at 75Amps, the actual current required to cause this kind of failure would be quite a lot more.
The most likely cause of this is physical damage to the cable, you say the meter cupboard was already open when you got to it, this suggests something has happened to open it.
 
is your tv amplifier led flat on the insulation? They kick out an awful amount of heat that over time could burn out the unit itself if not dissipated properly i.e not buried in fibreglass. As for the surge id be expecting extensive damage if one had occurred and im adamant the meter tails issue is coincidental
 
Where the 16mm cables were damaged they were touching each other and glowing red. There was nothing rough enough nearby that could have caused damage to the cables through abrasion.
I was too s**t scared when I saw what was happening that a photo was the last thing on my mind.
Agreed, thats not a place to hang about clicking pics !
I can only think the tails were subject to significant prolonged overload to melt the insulation off and allow them to contact each other. Or the tails had a defect in their insulation. They are each double insulated, but they can be damaged ...
 
Where the 16mm cables were damaged they were touching each other and glowing red. There was nothing rough enough nearby that could have caused damage to the cables through abrasion.
I was too s**t scared when I saw what was happening that a photo was the last thing on my mind.

There must have been some damage to the insulation of the meter tails I would have thought. It would have taken quite some overload elsewhere in the system to cause enough current to flow to melt the insulation to the point where it caused this failure, and if this was the case then there would be heat damage somewhere else as well, ie. at the location of the fault itself.

As said above, it's suspicious that the meter cabinet door was already open at the time.

Daz
 
and they tell us that aliens are not amongst us. just take a look at that jeremy corbyn. obviously from another planet.
 

Reply to Meter Tails Incident in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
720
During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away...
Replies
22
Views
5K
We had a new supply installed this week. DNO installed new cut out and fuse externally. Meter operator sent his engineer to move the meter in the...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock