could anyone please advice..
is it ok to run meter tails from an existing supply to a second board about 20meters away to supply a 8way split board wich will run 2 stand up sunbed capsules and a ring circuit and a lighting circuit..???
 
Scolmore Electrical Products
This official sponsor may provide discounts for members
D

DanBrown

  • Thread Starter Thread Starter
  • #2
Fusion, if you intend on installing a new set of tails into the henley blocks, you need to be aware that the maximum run for mains tails is only 3m. You could always fit an fused isolator next to the henley blocks, and come from that using swa or twin pvc etc to the new board..:)
 
F

fusion

  • Thread Starter Thread Starter
  • #3
thanks for that pal.would you use 10mm or 16mm..???
 
S

Spudnik

  • Thread Starter Thread Starter
  • #4
thanks for that pal.would you use 10mm or 16mm..???
Depends what your calcs have given.

Personally 16mm would be the way to go.