could anyone please advice..
is it ok to run meter tails from an existing supply to a second board about 20meters away to supply a 8way split board wich will run 2 stand up sunbed capsules and a ring circuit and a lighting circuit..???
 
Advertisement - Content continues below
D

DanBrown

  • Thread Starter Thread Starter
  • #2
Fusion, if you intend on installing a new set of tails into the henley blocks, you need to be aware that the maximum run for mains tails is only 3m. You could always fit an fused isolator next to the henley blocks, and come from that using swa or twin pvc etc to the new board..:)
 
F

fusion

  • Thread Starter Thread Starter
  • #3
thanks for that pal.would you use 10mm or 16mm..???
 
S

Spudnik

  • Thread Starter Thread Starter
  • #4
thanks for that pal.would you use 10mm or 16mm..???
Depends what your calcs have given.

Personally 16mm would be the way to go.

Better to have too much capacity than not enough.
 
Aico 3000 Range
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to meter tails in the Electrical Forum area at ElectriciansForums.net

Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom