Discuss Metrel MI3000 Zs(rcd) tripping in the UK Electrical Forum area at ElectriciansForums.net

gazdkw82

-
Arms
Reaction score
739
Anyone had any experience of metrel testers tripping an RCD when doing a Zs when you have the rcd no trip function on?

It happened the other day on my 2391 assessment but the college tester did the same so I assumed it was the college rig.

Just wired up a cooker for my niece, can't do a Zs. Tested the rcd and that's fine.

Pain in the rear.
 
We have five of them and have never had an issue trying to do no trip Zs.
 
Is the RCD part of a split load arrangement? It sometimes happens that existing and test earth currents add together to trip the RCD or RCBO, especially if the RCD is on the sensitive side. Have you ramp tested the RCD to see if it is on the sensitive side?
 
Last edited:
The RCBO might be on the sensitive side so worth ramp testing it to confirm that isn't a factor. It's also worth checking the tester on other circuits to see if it causes the issue with any RCD/RCBO as there is always the possiblity that it could be the problem or at least twards the extreme end of spec so will cause a trip most of the time.

You could always by pass the RCBO for the test by temporarly swapping it out for and MCB.
 
You need to change the meter settings so that it gives you the tripping current in mA as opposed to time (my old Metrel Eurotest XE has a ramp test option that allows for this). Most no testers no trip loop test will use a current of around 15mA so if the RCD is sensitive or your tester is for some reason pushing a current higher than 15mA then you are likely to end up with a trip.
 
Anyone had any experience of metrel testers tripping an RCD when doing a Zs when you have the rcd no trip function on?

It happened the other day on my 2391 assessment but the college tester did the same so I assumed it was the college rig.

Just wired up a cooker for my niece, can't do a Zs. Tested the rcd and that's fine.

Pain in the rear.
Are you using the three leads when taking the Zs?
 
Ha ha, I should never have read this thread. Today was downlight day. After 15 it feels like Groundhog Day but I still got the sore back, sore neck you name it. Anyway, part way through I'm up a ladder on the last downlight in a string. So I'm thinking now's the time for a "no trip Zs". Bleeping thing tripped the RCBO ... Swear I've never had that before. Re-set RCBO and no problem, trip - what trip? Jinxed I say, jinxed !!!
 
Ha ha, I should never have read this thread. Today was downlight day. After 15 it feels like Groundhog Day but I still got the sore back, sore neck you name it. Anyway, part way through I'm up a ladder on the last downlight in a string. So I'm thinking now's the time for a "no trip Zs". Bleeping thing tripped the RCBO ... Swear I've never had that before. Re-set RCBO and no problem, trip - what trip? Jinxed I say, jinxed !!!
bet your sausage fingers shorted something out the 1st time.

and 15 downlights? what did you do after morning coffee break?
 

Reply to Metrel MI3000 Zs(rcd) tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
733
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
186

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock