Electrical2Go - Online Electrical Supplier
Advertisement - Content continues below
Discuss MI 1mm and sheath for wiring conductors, advise in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
s1m0n
I am sitting my 2330 L3 rig next week, one circuit is in MI, the imformation supplied states for that circuit, under wiring conductors ( as in the Schedule of Test Results) they are Live/CPC as 1mm and sheath.
I have no idea what to write down for the CPC 'mm' size.
any advise will be great,
Instyle LED Lighting Specialists UK
G
Guest123
  • #3
In addition, I cant think of anywhere that I've ever seen values for the CSA of pyro sheath.:confused:
old dog
i had to look it up for my practical 2391 thats what i put down on the sheet but for the life of me i can,t
remember where i seen but it does make sence the same with swa i would think
G
Guest123
  • #5
Hey.
With regard to the swa, I always put "K" in the CSA box as this refers to the value of armouring CSA given in the book.
s1m0n
  • #7
Thanks Lenny and old dog,
so is K the item to entre, do you know what reference you found this in, so I can make reference in my course notes?
Thanks.:):)
G
Guest123
  • #8
IGNORE THE TABLE NUMBERS, IT'S AN OLD REFERENCE^^^^^^^
The values in GREEN comply with BS7671, the values in RED do not
With these values you can then use the adiabatic equation P128 BS7671 to double check conformity
Hope this helps.
uHeat Banner - Forum Discount Available
Reply to MI 1mm and sheath for wiring conductors, advise in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Bulk Workwear - Clothing Suppliers for the Whole Forum Network