as faras i know, yes, as long as its of sufficient Xsectional area to carry the calculated fault current.
 
agreed, but i think the op was concerned if you had to have an earth conductor in the cable as well. i've not used micc for years, it always was that the skin was earth then.
 
It's MICC, the outer sheath IS the earth! you cant isolate it from earth due to how it's terminated.

Yes, as Telectrix said, the OP was checking on the suitability of the sheath as a CPC.

The sheath is very good as a cpc but not always so if also a combined protective bonding conductor,

Table D11 in Guidance Note 1 has 'effective sheath CSA' values for many commonly available MICC types.
2L2.5 for example has a sheath equivalent of 8.2mm.
 
Yes, as Telectrix said, the OP was checking on the suitability of the sheath as a CPC.

The sheath is very good as a cpc but not always so if also a combined protective bonding conductor,

Table D11 in Guidance Note 1 has 'effective sheath CSA' values for many commonly available MICC types.
2L2.5 for example has a sheath equivalent of 8.2mm.

Have seen a chart somewhre which gives the CSA of the sheath similar to the SWA chart
 
thanks for the quick replies , i only ask as we have to install a 4mm 2C MICC cable and the spec calls for the earth to be used as the shealth. The pm says

Yes I believe that is why we are using 3 core this should be what has been priced because I don’t think 17th edition allows the sheath to be used but may be wrong.
 
yes the spec says earth used as sheath , but he says we need a 3C to use 1 C as earth because the 17th edition does not allow you to use the sheath as earth

Is this correct ?
 
'He' needs to read BS7671:2008 of course you can use the sheath, I posted the detail of the reference material supporting this!
 
Physical cross sectional area of MICC/PYRO copper sheath for use as CPC.


2L1 ****** 5.4 mm2
3L1 ****** 6.7mm2

2L1.5 ****** 6.3 mm2
3L1.5 ****** 7.8 mm2
4L1.5 ****** 9.1 mm2


2H1.5 ****** 11 mm2
3H1.5 ****** 12 mm2
4H1.5 ****** 14 mm2


2L2.5 ****** 8.2 mm2
3L2.5 ****** 9.5 mm2
4L2.5 ****** 11 mm2

2H2.5 ****** 13 mm2
3H2.5 ****** 14 mm2
4H2.5 ****** 16 mm2

2L4 ****** 11 mm2
2H4 ****** 16 mm2

2H6 ****** 18 mm2
3H6 ****** 20 mm2

2H10 ****** 24mm2
3H10 ****** 27mm2

2H16 ****** 30mm2
3H16 ****** 34mm2
 
cant use the sheaath as an earth what a numpty the pots come with the earth lead attached and look at lennys post ,how often do you see crossectional earths as good as that not in many twin and earths , 4mm twe 2.5mm cpc 4mm micc 11mm earth i rest my case
 
Last edited by a moderator:
as far as im aware you can use the outer sheath of the cable as long as you use an earth tail pot and not a standard one

Absolutely not true, earth pots were introduced for applications where glands were not used but a cpc connection was still required.

Conversely, good cpc continuity can still be achieved with a gland and standard pot.
 
It strikes me, that today's electricians are getting absolutly no training in MICC cables or in it's installation.
Yet install an installation in MICC today, ....and it will last forever, unlike any other form of wiring. Next they'll be calling it a ''speacialist'' wiring system!!! How times change, and as usual money is at the route cause of it!!
 
It strikes me, that today's electricians are getting absolutly no training in MICC cables or in it's installation.
Yet install an installation in MICC today, ....and it will last forever, unlike any other form of wiring. Next they'll be calling it a ''speacialist'' wiring system!!! How times change, and as usual money is at the route cause of it!!

Couldn't agree with you more! Its a shame we live in such an expensive world.....
 

Reply to MICC Cable Outer Sheath in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Hello Everyone. I'm surprised this subject does not get much attention. 'The elephant in the room' I refer to is the 'new rubber'. On new...
Replies
0
Views
208
I am making a lamp and I need to run the live, earth and neutral wires through a hole in 25mm mdf. The outer sheath is removed due to a switch...
Replies
10
Views
2K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock