I replaced a single socket for a double socket for a customer today, and whilst doing the IR tests noticed that the Line/Neutral reading was low.
The readings were:
L/N 0.95 Mohms
L/E 97.6 Mohms
N/E 87.4 Mohms
I checked and made sure that nothing was plugged in on the ring and noticed he had some smokes wired in. I told him I needed to disconnect them to do the test but he didn't want me to. So what do I do, how do I state this on the cert?
Thanks
Mark