Even if its not as per the regs ?? they recommend 25mm

I'd more more interested in making sure the earthing/bonding is correct.

What's the CCC of 16mm tails? ;)

If I was replacing a CU then perhaps you would but I don't see the point to be honest.

If the customer doesn't want to pay then why do it?
 
Bonding is fine and up to date, The 16mm tails will carry roughly 85 amp so im not bothered about that.. its a case of weather its acceptable to issue MWC if the tails are not as per the regs
 
Bonding is fine and up to date, The 16mm tails will carry roughly 85 amp so im not bothered about that.. its a case of weather its acceptable to issue MWC if the tails are not as per the regs

You wouldn't find me changing them, you've just proved yourself that they do not need to be. 16mm tails rated to 85A protected with 60A device, where's the issue?

What earthing system is the installation using?
 
Its a TNCS, just beating myself up with the regs as they state minimum 25mm

As I keep seeing posted recently, the Regs are Guidance Notes NOT LAW. In this situation you can safely justify why they do not need to be replaced especially as you are only doing a Minor Works. CU change? Fair enough but the customer has already stated that they do not want to pay for it.
 
I am fairly sure that the wiring regulations do not state a minimum size for the tails to a CU, I think this is stated in the on site guide which is certainly just a guide.
 

Reply to Minor Works and Meter Tails in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock