- Reaction score
- 0
On the report is the earth fault loop impedance internal Zs or external Ze ?
Discuss Minor works cert in the Electrical Forum area at ElectriciansForums.net
If it was wanting Ze it would say "External Earth Fault Loop Impedance"On the report is the earth fault loop impedance internal Zs or external Ze ?
OK
I have run my test on the furthest socket
LN PSC 0.29ohm 900A
L PE PFC 0.91ohm 253A
All circuits are protected by a 30mA RCD main switch.
Now for a lighting circuit I would usexpect calculated Zs = Ze + (R1+R2)
Ze = 0.17 ohm
R1+R2 = 0.25 ohms
Zs = 0.42 ohms
Is this correct ?
I have done the C&G 2392 test and Inspection fairly recently.
I am still feeling my way around and just wanted some reassurance.
This is a for an addition of sockets and light fitting.
2 separate jobs / MWC
A live oneIs this as a practice job at your own home or are you doing these jobs at a customer's house ?
Think I'll stay out of this.
The post wasn't a mistake I think you need a bit of guidance.Thanks !
Just not very confident, just didn't want to make a mistake.
Maybe posting was the first ?
Reply to Minor works cert in the Electrical Forum area at ElectriciansForums.net