Hi wondering if someone can advise me on something..

Im installing a few outdoor lights, will spur them off a ring via fused spur. question is when i’m testing do I take the max zs values of a 3/5a 1362 plug top fuse or zs at light fitting and use max zs for the mcb?

Please explain in detail, I’m a bit dyslexic

Regards

Big D
 
You would use the max Zs figures for the fuse (3A fuse to BS 1362 has max Zs 15.6 ohms on hot circuit) and measure it at the furthest light, but ideally check every light if there are a few on the outside circuit.

That is assuming that the point where the FCU is in the ring already meets the Zs for the MCB, but that ought to be the case unless you have an extraordinary length of cable.

Also the supply that is feeding the outside light should be RCD protected, any new (or recent) ring would have such RCD protection but check it does, and also test that the RCD trips and resets OK using its test button.

RCD protection would allow a higher Zs value to still meet automatic disconnection, as you generally have to do with a TT earthing arrangement, but if practical I would always aim to meet disconnection on the over current protection protection (MCB/fuse).
 
Last edited:
Realistically you should not be anywhere close to the max Zs for a 3A fuse.

For example, if you do the usual design and assume cold-measured cables at 80% of Zs then your maximum cable length for 1mm cable (44 ohm/km) is about 259m.

Ring final has max Zs which should be below 1.1 ohms to meet disconnection for a 32A B-curve MCB and that is your max "Ze" at the FCU
Fuse Zs hot = 15.6 ohms so 80% cold = 0.8 * 15.6 = 12.5 ohms
Max 1mm light cable R1+R2 = Zs - Ze = 12.5 - 1.1 = 11.4 ohms
Max new 1mm cable length = 11.4 / 0.044 = 259m

It is also doubtful that the light cable would run hot, certainly nothing like 70C, so you have some additional margin for disconnection.

Depending on the load you might run in to voltage drop problems before the maximum Zs length, but if only a couple of 30W or 50W lamps then probably not.

Basically your dead measurement of R1+R2 and/or live measurement of Zs at the furthest light is more above verifying the circuit has been properly implemented.
 
Last edited:

Reply to Minor works testing FCU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Hi, quick question. How do FCU's work? Do they just protect the load side and what I mean is, say you have a ring final with 2.5mm^2 protected by...
Replies
9
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock