haj

-
Arms
Reaction score
47
Good evening gentlemen upon testing a radial socket circuit on a type b 16 amp mcb i discovered the cpc was open between cu & first socket or what i thought was the first socket the house has been knocked about by various people i think maybe an old socket has been removed or a jb in the wall maybe.I think a new cpc direct from cu to first socket is the best answer as the owner does not want any damage to the new walls that the old t&e goes through, he asked if it was possible to borrow an earth from the other socket circuit as they run side by side on the landing and it has a jb in it not a good idea i said what do you all think ?
cheers
 
If it's been knocked about as much as you say.It sounds like it would be better to re-wire it.How many sockets are on this so called radial:confused:Have you tested the ring yet?
 
Last edited by a moderator:
there are 9 sockets on the circuit and the cpc is ok from first socket onwards.there are only two radial circuits and 1 kitchen ring.
cheers:)

the kitchen ring is on a seperate cu on its own.
 
Last edited:
there are 9 sockets on the circuit and the cpc is ok from first socket onwards.there are only two radial circuits and 1 kitchen ring.
cheers:)

the kitchen ring is on a seperate cu on its own.
Definitely wouldn't take an earth off another circuit.Can't you pull a leg from the board to the first socket
 
thats the plan i just wanted to know what the views are on borrowed earths ? am going to sneak an earth direct from cu with as little damage as poss may have to take a long route to get there.
 
One option would be to disconnect the radial at the CU and supply it via a fused spur from the ring. This may not be ideal but it could be the only alternative to some more extensive rewiring.

If you are considering replacing the just cpc then is it worth completely replacing the twin & earth to the first socket? If the cpc is damaged or badly joined somewhere then what about the line & neutral? Have you tested them?
 
One option would be to disconnect the radial at the CU and supply it via a fused spur from the ring. This may not be ideal but it could be the only alternative to some more extensive rewiring.

If you are considering replacing the just cpc then is it worth completely replacing the twin & earth to the first socket? If the cpc is damaged or badly joined somewhere then what about the line & neutral? Have you tested them?
There isn't a ring in the property,well there is but it only feeds the kitchen.Rest of the house is fed via 2 radials:confused:Forgot to add this,if you spur off a ring,you can only add 2 sockets max
 
Last edited by a moderator:
When asked about taking the cpc from a nearby socket circuit, I assumed it was from a ring. If, on the other hand, the second circuit is a radial then to come from this circuit instead of from the CU would only be extending the radial. It's perhaps not good practise to split a radial into 2 branches but the regs don't seem to mind (appendix 15, page 363).

P.S. As i understand it, an unfused spur from a ring (2.5 mm T&E, 32A MCB) can only supply one single or double socket outlet. To come from the ring via a 13A fused spur, you can feed as many socket outlets as you like (provided the cable is not too long for voltage drop to become an issue).
 
Last edited:
replacing the whole t&e is not poss without damaging the proprerty and customer said no.L&N Are ok so i guess it must be joined out somewhere and the cpc is out..
cheers lots of thoughts as usual.:)
 
Is it not possible to disconnect the existing feed to this circuit & refeed it somewhere else along the circuit?, that way you may find a route that does not damage the building fabric, or if it'san upstairs circuit a JB. Cheers, Matt
 

Reply to missing earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
771
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
405
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
676
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
240
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
780

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock