stuarth

-
Arms
Reaction score
84
I have a brand new MK 63amp RCD that fails Ix5 test everything else tests fine on the board, I tested with all circuits off everything unplugged so swapped it for another thinking must have a faulty one but the same result, it will trip at 50ms and ramp tested at 33ma, ze=0.18 what could be happening? any advice on what could be wrong would be greatly appreciated.
 
It is failing to disconnect at 40ms
 
30ma
 
I did test with another tester with exactly the same results.
 
Ok, will try tomorrow if I can get access again, what is your thinking with disconnecting outgoing?
 
You are isolating it from any other influence, just switching off the protective devices only eliminates the line conductors.
 
Assuming isolating the neutral works what do I do to correct it? there are two existing RCBOs on the board which work well within the regs which I disconnected to test if influencing the RCD, they did not.
and you have left a fault rcd,tut tut.
not sure how much more dangerous a RCD tripping 10ms slower is but will be going back armed with more knowledge and tips on correcting it.
 
Could it possibly be partial hysterisis of the toroidal coil? Maybe there is some DC current causing this??? Maybe you need an A type instead of AC, just a stab in the dark there....
 
domestic, unable to get in today but should on monday
 
There’s no requirement in the 18th edition for RCDs to trip in any particular time.

As for this testing with all loads disconnected, what’s that all about?
Yes Mrs Miggins, your RCD works fine, as long as you don’t switch anything on.
 
There’s no requirement in the 18th edition for RCDs to trip in any particular time.

As for this testing with all loads disconnected, what’s that all about?
Yes Mrs Miggins, your RCD works fine, as long as you don’t switch anything on.

The note in 643.8 makes reference to compliance being achieved in terms of additional protection when the 40ms at 5x rating is met.
I just see that this information has migrated from section 415 and found a new home.
 
The note in 643.8 makes reference to compliance being achieved in terms of additional protection when the 40ms at 5x rating is met.
I just see that this information has migrated from section 415 and found a new home.
Yes, but it’s a note not a requirement.
The requirement now, is just to have 30mA RCD protection
 

Reply to MK 63amp RCD that fails Ix5 test everything else tests fine on the board in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock