- Reaction score
- 5,808
My wife is on the committee of the local village, and they have just had an EICR carried out. This came out as 'unsatisfactory' and accompanied by a quote for remedials totalling well north of £9000, although this does include a fire alarm system (which, AFAIK, no one has suggested is required).
A number of the c2s refer to tails to two DBs being undersized.
The supply is single phase 100A, with the metering equipment in an external box. 25mm2 tails go through the wall to a 100 switch fuse, and from there more 25mm2 tails go through the roof of an extension to a point in the main hall where the meter was originally fitted. Henley blocks then distribute the power to four DBs.
25mm2 tails go to the two 'main' DBs, sited next to each other, and this is all deemed satisfactory.
Two other smaller DBs are also fed from the Henley blocks in 16mm2, and both of these are coded C2 as under rated for the designed load.
Tails to one are in surface mounted trunking, so method B, and the load comprises a small number of lights on a 6A MCB, a single 2G 13A s/socket on a 16 MCB, and two 32A blue sockets, each on a 32A MCB. Main switch is a 30mA RCD. (
32A sockets are for two stage lighting controllers, sold to them and installed by some shyster, with the aid of a grant, many years ago. They have precisely three stage lights, so the total load has never exceeded around three amps, and one 32A socket has never been, and never will be, used)
The other DB on 16mm2 tails has these running through a short length of the roof space, so Method A.
Load on this DB are some lights on a 6A MCB, a RFC on a 32A MCB, and a 3kW water heater (fixed load of 12A) on a 16A MCB. Main switch is, again, a 30mA RCD.
Comments, please.
Comments, please.