R

Richard3009

I have found in my house on the downstairs ring main that three lives are terminated into the 32A circuit breaker, two are for the ring main as you would expect; the third is for a socket below the fuseboard, to all intents and purposes its just a spur and electrically wise its sound.
Just wondered how this stands up with regs having three conductors in the breaker.
 
my understanding of the regs, from memory mind, is that a spur can originate from a termination at a socket outlet, a junction box or at the origin of the circuit.
 
yes, would agree with wetstring - it is acceptable to have a spur on the circuit from the consumer unit in this way.
Never done it on sockets, but it is a good way of adding an outside light on a lighting circuit if there are no spare "ways" in the consumer unit.
 
then i would see that individual socket as more of a radial being served directly from the breaker in this way and i wouldnt have a 32 amp radial on a 2.5 t/e :confused:
 
if i was designing a circuit being fed from an mcb directly to a socket irrespective of what other cables were in the mcb already i would see that circuit as a radial, not a spur.
26a cable and 32a breaker :confused:.
i see where your coming from spurring from existing socket etc etc but not from board.
just my opinion ;)
 
the regs permit it, any spur is a single 2.5mm cable protected with 32A breaker
 
Last edited by a moderator:
its not a radial, you can't have more than one double 13A on it, a radial you can providing the conductor size is correct for the potential load.
 
didnt mean you tiger, was asking richard. ;)

dont forget Ib has to be equal to or greater than In when selecting a cable richard.

point me to the correct reg and i will stand corrected :confused:
 
If there was a radial circuit from a 20A MCB then thats fine

If there was a "spur" from a 32A RFC MCB then that is also fine.

It is no different at all to taking a spur off the back of a socket or at any point in the ring via jb.

Pg 362/3
 
the spur should only feed one outletunless fed through 13afcu so max current via 13amp plugs, 26amps.
 

Reply to More than one circuit on breaker in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock