First of all, sorry I didn’t take more photos.
Been to a customer to price a job and had a look at his CU. Split RCD half and half.

From this picture, it appears the left hand side rcd is off, although all the circuits are powered.

3EC34DE8-5E70-4955-91FE-22533653AEF1.jpeg

so. First thought, faulty rcd. Says it’s off but contacts must still be closed.

Further investigation. Turned all breakers off, reset rcd and it held. Tripped on test button.
Reset right hand rcd.... also held.
Turned on circuit 1, which is marked as sockets, (first one off right hand, not in picture) trips LEFT hand rcd.

Without detailing any more, it appears the left hand side bank of breakers are being supplied through the right hand side rcd. Possibly because they’ve mixed up the rfc legs. All the load on the left hand side running through one 2.5mm cable. I think I’ll clamp it out of interest.
Would this happen with just lives mixed, just neutrals, or both?

I’ll update early next week. With more photos
 
"do not megger alarms". a niceic approved sticker. can't they get terminology correct? and it's pi$$ed.
 
"do not megger alarms". a niceic approved sticker. can't they get terminology correct? and it's pi$$ed.
Looks more like an AICO sticker (maybe NIC approved) but def an Aico sticker that is included in the detector box.
[automerge]1594972619[/automerge]
Would this happen with just lives mixed, just neutrals, or both?
Please post your findings, I'm sure we would all like to know the outcome!
 
I would check the neutrals first, especially the rcd neutrals are on the correct neutral bars. Came across something similar a couple of years ago. You could also check the legs of any ring mains are not crossed over.
[automerge]1594975810[/automerge]
When it says do not megger alarms, it's not talking about the brand of tester. It's telling you not do a Insulation Resistance Test on the alarm circuit as it is vulnerable to the test voltage.
 
Last edited:
I would check the neutrals first, especially the rcd neutrals are on the correct neutral bars. Came across something similar a couple of years ago. You could also check the legs of any ring mains are not crossed over.
[automerge]1594975810[/automerge]
When it says do not megger alarms, it's not talking about the brand of tester. It's telling you not do a Insulation Resistance Test on the alarm circuit as it is vulnerable to the test voltage.
Welcome to the forum. We know I was being sarcastic, for a manufacturer to state "do not megger" is pretty poor terminology.
 
The implication of the label is that it is not O.k use an insulation tester manufactured by Megger, but by default it would be acceptable to use any other make tester to carry out an Insulation test.

As Westwood, it's wrong for any manufacturer to use that term.
 
Do not “megger” alarms, hear you loud and clear through the “klaxon” and remember to clean up afterwards with the “hoover”

After you've parked up outside on the "tarmac" make sure to take notes with your "biro" about what you find inside. Hopefully it's not a handful of discarded "fibreglass" insulation or "bubble wrap". Take care not to break those flimsy Hager lids or you might have to fix it with "super glue" "sellotape" or "velcro"
 
"do not megger alarms". a niceic approved sticker. can't they get terminology correct? and it's pi$$ed.
Why do you think NICEIC approved this? It's Aicos own sticker?

I've mentioned it to Aico a couple of times that there is no such test as 'meggering'. I dont think they can spell insulation :tearsofjoy:
 
After you've parked up outside on the "tarmac" make sure to take notes with your "biro" about what you find inside. Hopefully it's not a handful of discarded "fibreglass" insulation or "bubble wrap"....

Never knew that "fibreglass" was a brand name - some more new information for today :thumbsup:

It does seem pretty unprofessional for a company like Aico to use a brand name in place of the correct term. Maybe they hope to start a trend and this is a subtle way of encouraging electricians to reference "Aicos" in place of "smoke detectors" ?
 
I think one person briefly attempted an explanation about littlesparks post, every other post has been about a sticker! :D
 
Turns out there is a connection between the 2 rfc's. One on each RCD.
The left hand side one is a pair... identical end to end readings on L and N
The right hand side however is not an rfc at all. Theres 3 legs here that are not connected to each other.. so not an rfc. One is an outside socket thats been added. Can trace that cable visually.
Another leg has a connection to the rfc on the left hand side. (i need to find this. could behind a socket, or in a jb)
The last leg has no connection to anything else. This could be a single spur, or it could be a radial with several points on it.

I'm going back with a few 16A breakers to try and split it down a little.
 
Never knew that "fibreglass" was a brand name - some more new information for today :thumbsup:

It does seem pretty unprofessional for a company like Aico to use a brand name in place of the correct term. Maybe they hope to start a trend and this is a subtle way of encouraging electricians to reference "Aicos" in place of "smoke detectors" ?
Aicos are the way forward every year I do an expert installer course with Aico which I’m sure most of you do. This is another topic which sparkys on here will disagree with me because smoke alarms don’t constitute an unsatisfactory report in an EICR because they are not “relevant” in our reports but I disagree if I see a battery only smoke alarm (fire angel) I get my hammer out and smash it off the ceiling. Every property should have a mains wired optical smoke alarm (hallway, landing) heat alarm kitchen interlinked with 10 year lithium back up battery. All my Scottish and Irish friends should know this as their laws are more robust compared to us welsh and English although we will soon be following you
 
Turns out there is a connection between the 2 rfc's. One on each RCD.
The left hand side one is a pair... identical end to end readings on L and N
The right hand side however is not an rfc at all. Theres 3 legs here that are not connected to each other.. so not an rfc. One is an outside socket thats been added. Can trace that cable visually.
Another leg has a connection to the rfc on the left hand side. (i need to find this. could behind a socket, or in a jb)
The last leg has no connection to anything else. This could be a single spur, or it could be a radial with several points on it.

I'm going back with a few 16A breakers to try and split it down a little.
A 3 legged ring. Apart from the difficulties in testing it, what danger might there be in putting all 3 legs on the same 32A breaker?
[automerge]1595382036[/automerge]
This is another topic which sparkys on here will disagree with me because smoke alarms don’t constitute an unsatisfactory report in an EICR because they are not “relevant” in our reports but I disagree if I see a battery only smoke alarm (fire angel) I get my hammer out and smash it off the ceiling. Every property should have a mains wired optical smoke alarm (hallway, landing) heat alarm kitchen interlinked with 10 year lithium back up battery.
Which code do you give for a battery only smoke alarm a) before and b) after you've knocked it off the ceiling with your Coventry screwdriver? And which regulation do you reference to justify said coding and remedial action?
 
Last edited:

Reply to Most obvious fault here in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi All, Would be grateful for some advice. Would like to add an additional light (Undercabinet 8W LED Batten light) to a two-way light switch...
Replies
7
Views
587
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
291
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock