Hi all, thanks again for any input.
I have been asked to look at this starter as motor starts ok, but when switches over to run motor stops and starter just hums.
First of all like I’ve said in previous posts I haven’t had a lot of experience with motors/ starters etc
Am I right in thinking this starter is for a capacitor start - capacitor run motor with no centrifugal switch as it has a timer set to 15 seconds and then 3 contactors?
The motor starts ok and contractor in middle kicks in and contractor on right kicks in but after time delay right contractor drops out, but left one doesn’t kick in.
The part I’m not sure about is that there is a 1M ohm resistor across the 13 and 14 contacts on the left contractor and if I bypass this with some cable it all appears to work fine. I have checked resistor and it reads 1M ohm like it should ( brown, black, green and gold).
Could anybody tell me why the resistor is there in the first place and what it does ( is it to stop a back feed?) and why the starter seems to work fine when I bypass it yet it is reading ok?😕😕
Thank you
Post automatically merged:

Also forgot to mention there is a cable from 14 terminal to A2 of run contractor..
 

Attachments

Last edited:
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Can you show a pic of the motor and it's rating plate. Have you looked at the piece of paper wedged in the back of the enclosure.
 
Last edited:

davesparks

-
Mentor
Arms
Esteemed
Is it definately a single phase starter and motor?
My guess from the picture and description woukd have been that it's a star delta starter.
 
  • Thread Starter Thread Starter
  • #5
It’s definitely 240v as no 3 phase on the farm. Capacitor’s are in the motor terminal housing. If it was a dodgy capacitor surely it would be the same even when bypassing the resistor?
I’ve found a drawing now, but struggling to read. If anyone could guide the stages of the starter that would be brilliant. Thank you
Post automatically merged:

D222324C-30C3-4BAB-A387-92C2E92CE5F4.jpeg8D00C077-B1EC-4CF7-9CAA-5EFF19C7637E.jpeg4E9CF641-42A4-4CAC-AEF5-5297F0942131.jpeg0E5BD1CC-C188-4841-ADF6-94BE41B379C9.jpeg
 
Was going to ask if it was a farm. Sounds like someone has made a two stage starter. What is the motor running is it a heavy load.
 
  • Thread Starter Thread Starter
  • #7
Motor plate etc.
Post automatically merged:

Yes it’s a large motor for the grain. What are the advantages of a 2 stage starter compared to a dol? I presume reduces starting current, but how. Thank you
Post automatically merged:

Sorry to ask so many questions, but could somebody explain what is the difference between a series parallel motor and a capacitor start/ capacitor run motor as well please? Thank you
 

Attachments

Last edited:

Lucien Nunes

-
Mentor
Arms
Esteemed
It seems that what you are seeing as a 1M resistor is actually the NTC thermistor (aka Brimistor which was a trademark of STC). Its function is to slightly delay the operation of RN to ensure a full open transition. Bypassing it, as suggested in note 1 for lower power motors, simply causes RN to operate immediately. If the starter works with it bypassed, the Brimistor itself is probably faulty.

If anyone could guide the stages of the starter that would be brilliant.
OK, you asked.

Before we start:

a) Series-parallel starting refers only to the connection of the run / main winding. It is the equivalent of star-delta starting but for single-phase, in that it lowers the voltage across each winding to reduce the starting current until up to speed, without the use of resistors or transformers. The start winding configuration and capacitor arrangement is a separate consideration.

b) There are two aspects to the start-run transition; switching the two run windings A1-A2 and A3-A4 from series to parallel, and disconnecting the start capacitor.

c) There are two possible capacitor configurations; capacitor-start induction-run, in which the capacitor winding is completely disconnected in run, and capacitor-start capacitor-run, in which the winding is disconnected from the start capacitor but remains in circuit via the run capacitor.

d) There are two possible centrifugal switch configurations; either it switches the start capacitor directly (in which case the starter timer is only responsible for the series-parallel transition) or it controls the ST contactor, in which case that contactor controls both the series-parallel connection and the start capacitor.

e) ST4 and RN2 are mutual interlocks that prevent ST and RN operating at once, which would short the main circuit L-N.

Pre-conditions for starting:
a) C2, RN2 and TM2 are all closed, i.e. the starter is not already in either the starting or running state and the timer is reset.
b) If the centrifugal switch is in the control circuit, it must be closed, i.e. the motor is not at speed.

START BUTTON PRESSED
Start button energises ST and TM

ST OPERATES. TM BEGINS TIMING
ST2 prepares a holding circuit for ST and TM, ready for when C2 opens
ST3 energises C
ST4 opens to prevent RN operating
ST main contacts 3-4 and 5-6 connect run winding terminals A2-A3 for series starting
ST main contact 1-2 connects start capacitor circuit (if controlled by starter and not directly by centrifugal switch)

C OPERATES
C2 opens to leave ST held only on ST2
C3 prepares a holding circuit for C, ready for when ST3 opens
C main contacts connect motor to mains

MOTOR RUNS UP TO SPEED
Motor run windings are in series, capacitor winding is in series with start capacitor (if CSIR) or start and run capacitors in parallel (if CSCR)]

TM TIMES OUT (OR CENTRIFUGAL SWITCH OPENS IF IN CONTROL CIRCUIT) WHICHEVER IS FIRST
TM2 or centrifugal switch disconnects ST

ST RELEASES
ST2 opens ST's holding circuit and disconnects TM.
ST3 opens, leaving C held only on C3
ST4 closes to energise RN via Brimistor.
ST main contacts disconnect run winding series connection and start capacitor.

BRIMISTOR HEATS UP
Brimistor resistance falls in a second or so, to the point where it is low enough for RN to operate.

RN OPERATES
RN2 opens to lock out ST
RN3 closes to bypass Brimistor
RN main contacts reconnect run windings in parallel

IF CENTRIFUGAL SWITCH IN MAIN CIRCUIT, IT OPENS
Start capacitor disconnected

Motor is now in running state.

No TL;DR option here. Either you follow it or you don't!
Post automatically merged:

Re. your specific motor, it's hard to tell from the pics. What I think I am seeing is that the two capacitors are in parallel, making it CSIR, and that there is no centrifugal switch. Therefore, the start winding is controlled by ST and disconnected under timer control at the same time as the series-parallel transition. The maximum timer setting is limited by the start capacitor duty cycle as noted in the instructions.
 
Last edited:
Correct me if I am wrong but the motor plate indicates it has always been connected to a two stage starter, the original probably having a manual start to run handle.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
Agreed, Stimmt, D'accord.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
@dlt27 How did you get on? Did you find out anything about the NTC or leave it bypassed?
 
  • Thread Starter Thread Starter
  • #12
Where could I find a brimistor to replace the existing one. I’m struggling to find one.
Many Thanks
Post automatically merged:

This is the what I thought was a 1M ohm resistor that I bypassed. Could it be a brimistor? Thank you
Post automatically merged:

 

Attachments

Last edited:

Lucien Nunes

-
Mentor
Arms
Esteemed
That, as you say, is a regular 1MΩ 1W carbon film resistor. But 1MΩ is too high to serve any useful purpose in the starter that I can think of, so I am not sure why it is there. However, looking at where the heat shrink sleeves meet the resistor body, there appear to be solid wires poking out with round flat bits on the end or possibly loops, and traces of a black substance. That would have been the Brimistor, a black rod of NTC material between those two ends. They do sometimes crack apart with age.

First, do you need it? Note 1 on the drawing states it is not needed for units below a certain current rating that I can't read, which probably have different contactors fitted. See whether the present application is above or below that figure.

Next thought, Brook Crompton still exist, I'd give their technical dept a call. They might be able to supply one from stock, or advise a modern equivalent NTC to replace it. Brimistors were just one popular manufacturer's range of NTC's, it doesn't have to be a Brimistor.

NTC's are still available and used in various electronic applications. There are a few dozen standard types, that have different resistances, current ratings etc. Much the same as the Brimistors of old, which were sold in a range of ratings more usually targeted at jobs like limiting inrush in AC/DC valve radios and TVs. If we have to, we can select something suitable ourselves.
 

marconi

-
Mentor
Arms
Esteemed
I think the 1 MOhm 1W resistor is used to provide mechanical rigidity in the flexible link so that the Brimistor can be placed across it, thereby reducing flexing stress which might damage the fragile end connections of the Brimistor. Without the resistor all the flexing stress is applied to the Brimistor leads. 1MOhm because only a tiny current flows through it so does not change the circuit's operation.
 

Lucien Nunes

-
Mentor
Arms
Esteemed
That sounds reasonable, I have done similar.TBH I had expected the original arrangement to have been a bit more sophisticated like a slice of tagstrip, as the bare ends of the Brimistor can't have been left flapping around. I assumed this was a retro-bodge but perhaps not.
 
  • Thread Starter Thread Starter
  • #17
Thanks again. Could anybody send a link for a thermistor/ brimistor that I could use to replace the faulty one..
 

marconi

-
Mentor
Arms
Esteemed
I did some rough calculations which indicate you need a brimstor or ntc thermistor with a cold resistance of about 2500 Ohms. I struggled to find a surge current limiter that might substitute because the max cold resistance I have found so far is 120 Ohms. It would be clumsy to put 20 of these in series. maybe my sums, oiled by half a bottle of Muscadet are wrong.

I did find some old brimistors for sale with a resistance of 3000 ohms.
Post automatically merged:

Brimistor CZ1 3000 Ohm 20°C STC Thermistor (Rare) | eBay - https://www.ebay.co.uk/itm/Brimistor-CZ1-3000-Ohm-20-C-STC-Thermistor-Rare-/112790433533

THis one drops its R to circa 300 Ohms or lower when hot. Of course it is eventually short circuited but one should not assume that.
 
Last edited:

Lucien Nunes

-
Mentor
Arms
Esteemed
My hunch is that the delay on a CZ1 will be too long. I'm not near my STC data book but I think they were popular for 100mA series heater chains, in which they give a gentle 10-20 second warmup. The original part in the starter looks like it had much lower thermal mass, so if the resistance and hence dissipation on 230V is similar, the delay would have been much shorter.

My other hunch is that when a call to Brook Crompton will either get one in the post for a few bob or they'll say 'we always tell people to bypass them, they were never really needed.'

@dlt27, were you able to confirm the motor FLC as per note 1?
 

marconi

-
Mentor
Arms
Esteemed
http://www.electrojumble.org/DATA/STC_Thermistors_Gen_Info.pdf

Just for information and interest.

(I assumed a 5VA coil (12500 Ohm 0.02A)which when closed mainly inductive with x 10 surge when mainly resistive (1250 Ohm 0.2A). NTC R reduces required initial closing surge current to a 1/3 until hot (0.07A). Warm up time of 2s. Required energy absorption rating 20J (= 2 seconds warm up from ambient x 10W power dissipation during this period). R of NTC at ambient is (250/0.07) - 1250 = 2300 Ohms.)
 
Last edited:

marconi

-
Mentor
Arms
Esteemed
I think I would avoid using a thermal delay - they do get hot and in this application are only taken out of circuit if the contactor auxiliary NO contacts by pass it. Use modern technology.

Here is a suggestion. Use a delay on relay:

RS PRO ON Delay Multi timer, Screw, SPDT, 12 → 230 V ac/dc | RS Components - https://uk.rs-online.com/web/p/products/1026124/

This is a 'cheap' one but there are gucci more expensive makes too. You would wire its A1 to RN3 13 and A2 to RN1 A1. You then use the NO contacts - delay On so they don't close until the delay has elapsed - to connect across RN3 13 and 14. You then set up the required delay on time - a few seconds and carefully position the relay inside the enclosure. On the side of the relay I would write with a permanent pen the purpose of this timer and the delay time.
 